Where are you guys finding these specific methods of "proving" the adequacy of 
the fire flow requirements? I don't find any language close to this in the IFC. 
 

Mark at Aero
602 820-7894

Sent from my iPhone

> On Dec 5, 2014, at 7:55 PM, "Steve Leyton" <[email protected]> wrote:
> 
> At 4 hydrants simultaneously if they're on the same water supply, or in 
> combination of public and private or at however many hydrants you have if 
> fewer than 4 and those being the sole source of fire flow.
> 
> As other comments, I would reiterate that the Table B fire flow is for 
> outside hose streams only and completely separate and apart from any 
> hydraulic demand related to building sprinkler systems.
> 
> Steve L.
> 
> 
> 
> 
> <div>-------- Original message --------</div><div>From: [email protected] 
> </div><div>Date:12/05/2014  6:29 PM  (GMT-08:00) </div><div>To: 
> [email protected] </div><div>Subject: Re: A Poll of the 
> Experienced </div><div>
> </div>I think I agree with you, but to be very specific, let's assume I'm 
> designing a new building on a greenfield site which is served by a public 
> water system. The building is type V construction, 600,000 square feet and 
> fully protected with ESFR sprinklers. Table B105.2 indicated a fire flow rate 
> of 8000 GPM, reduced to 4000 GPM for sprinkler credit, at minimum 20psi. My 
> question is, WHERE is this 4000 GPM at 20 psi measured? At the city water 
> main connection? Or at the fire pump discharge? 
> 
> Mark at Aero
> 602 820-7894
> 
> Sent from my iPhone
> 
>> On Dec 5, 2014, at 7:17 PM, "Cahill, Christopher" <[email protected]> 
>> wrote:
>> 
>> Neither.  It's the flow you need for a building. You might get it from a 
>> muni or private. Absolutely nothing to do with sprinklers except you get a 
>> reduction if building is sprinklered.
>> 
>> 
>> Chris Cahill
>> Fire Protection Engineer
>> Burns & McDonnell
>> 952-656-3652
>> [email protected]
>> 
>> 
>> -------- Original message --------
>> From: [email protected]
>> Date:12/05/2014 8:12 PM (GMT-06:00)
>> To: [email protected]
>> Subject: A Poll of the Experienced
>> 
>> Over this weekend I'd like to ask the opinion of those forumites experienced 
>> in the reading and understanding of the "International Fire  Code" on the 
>> topic of "Fire Flow" described in Chapter 5, and further prescribed in 
>> Appendix B. Is the available flow rate and residual pressure referenced, 
>> intended to describe these values of the municipal or private water supply 
>> available to the building site? Or, the minimum output of any fire pump 
>> associated specifically with the automatic sprinkler system in the building?
>> Any takers? Questions? Clarifications?
>> Thanks for any answers.
>> 
>> Mark at Aero
>> 602 820-7894
>> 
>> Sent from my iPhone
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to