You are being asked to mix apples and oranges. See 24.1 of 2010 edition if 13. 
You are certifying the system to 13. The inspection reports are to 25. Two VERY 
different things.

R/
Matt

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steven Cook
Sent: Thursday, December 18, 2014 3:00 PM
To: [email protected]
Subject: Test Certificates

I am looking for some guidance pertaining to completing test certificates.  
Without giving specifics as to building location - here is the summary:  We are 
working in a very large facility with multiple systems, pumps, etc.   The 
property is large enough to have their own in-house facilities / engineering 
crews that operate the valves, or drain individual floors and restore to 
service upon completion.   As part of final closeout / acceptance of the 
project, we typically provide a test certificate.   The problem I am having is 
at this property, where we don't operate the valves, the facilities people are 
not allowing us to do a drain test or verify the time to operate the alarms.   
Older building, no gauges on the FCVAs.   I have tried to just leave these 
lines blank or even indicated on the test certificate these items weren't 
tested but the fire department won't accept it (issue CO).  The facility is 
indicating we should just be copying the information over from their (self-
 performed) quarterly inspection reports.   We will not do so WITHOUT clearly 
stating the info was copied from the inspection report, which the fire 
department has already indicated is unacceptable.   Obviously circumventing the 
intent of the testing.    Tough spot - being told the typical "everyone else in 
here copies it".

I am looking for the language in NFPA 13, 25, etc that I can use to 
substantiate my position.   Common sense explanation isn't getting it done.  No 
explanation as to why we aren't allowed to get these readings.   I want the 
specific code language to have as back-up before I explain to these guys we 
might be all done working for them.

Help is greatly appreciated.

Steve Cook
Sprinkler Operations Manager
TG Gallagher

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to