Steve:

I agree with what you stated you are being asked to do - falsify a document. I come across that from time to time. I just basically tell my customers that I don't really care what the others before me did. I will only do what I believe is correct and that I won't jeopardize my reputation or integrity for any amount of money or for any customer. Stick to your guns. If they won't respect your integrity, you may want to rethink your relationship with them.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 12/18/2014 4:38 PM, Steven Cook wrote:
Matt,

Will review section reference when I get back in front of computer.   Agree.  
Two completely different things.  Basically, being asked to produce fraudulent 
document stating we performed a test (drain and alarm) that we didn't.  Let's 
call it what it is.  The above test certificate contains a line for this data.  
If I'm not doing these test, I'm not filling in the lines with data from their 
quarterly inspection reports, falsely indicating I did.  Looking for code 
reference stating test is even required when working on a system.

Steven Cook
TG Gallagher
Sprinkler Operations Manager

Sent from my iPhone

On Dec 18, 2014, at 5:11 PM, Matt Willis 
<[email protected]<mailto:[email protected]>> wrote:

You are being asked to mix apples and oranges. See 24.1 of 2010 edition if 13. 
You are certifying the system to 13. The inspection reports are to 25. Two VERY 
different things.

R/
Matt

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steven Cook
Sent: Thursday, December 18, 2014 3:00 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Test Certificates

I am looking for some guidance pertaining to completing test certificates.  
Without giving specifics as to building location - here is the summary:  We are 
working in a very large facility with multiple systems, pumps, etc.   The 
property is large enough to have their own in-house facilities / engineering 
crews that operate the valves, or drain individual floors and restore to 
service upon completion.   As part of final closeout / acceptance of the 
project, we typically provide a test certificate.   The problem I am having is 
at this property, where we don't operate the valves, the facilities people are 
not allowing us to do a drain test or verify the time to operate the alarms.   
Older building, no gauges on the FCVAs.   I have tried to just leave these 
lines blank or even indicated on the test certificate these items weren't 
tested but the fire department won't accept it (issue CO).  The facility is 
indicating we should just be copying the information over from their (sel
f-
performed) quarterly inspection reports.   We will not do so WITHOUT clearly stating the 
info was copied from the inspection report, which the fire department has already 
indicated is unacceptable.   Obviously circumventing the intent of the testing.    Tough 
spot - being told the typical "everyone else in here copies it".

I am looking for the language in NFPA 13, 25, etc that I can use to 
substantiate my position.   Common sense explanation isn't getting it done.  No 
explanation as to why we aren't allowed to get these readings.   I want the 
specific code language to have as back-up before I explain to these guys we 
might be all done working for them.

Help is greatly appreciated.

Steve Cook
Sprinkler Operations Manager
TG Gallagher

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to