Change to mandatory relief valve was in 2010.   

SL



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Aaron Peck
Sent: Wednesday, January 07, 2015 3:46 AM
To: [email protected]
Subject: Pressure Relief Valve on Wet Pipe System

I wonder if I've been doing it wrong all along since 2010, but NFPA 13,
2013 Ed. 7.1.2.1 require a pressure relief valve on ALL wet pipe
sprinkler systems? I can't tell you how many times in the past none have
been installed. Granted they might not have been all designed according
to 2010+, but just surprised this hasn't jumped out at me before.

 

Looking back the 2007 code mentions only in "gridded wet pipe systems"
then
2010 eliminates the word "gridded" as well as the 2013 code reads the
same as 2010. What's strange is my 2010 Hand book doesn't denote that as
a changed section, actually none show up. Does the Hand book remove
those that are there in the standard version?

 

Well I learned something knew.