Speaking of....

13-2016 (Proposed)
7.1.5 (Proposed) - Air Vent Requirement (single) for all wet pipe systems
8.16.6 (Proposed) - 1) 1/2" manual valve (min) 2)Automatic Air Vent 3)Other 
Approved Means
http://digital.turn-page.com/i/434573/10

20-2016 (Proposed)
 http://digital.turn-page.com/i/434573/14

FYI 

Dan


Dan Wilder | Project Manager-Design-BIM-QAQC | WSFP.COM 
Western States Fire Protection
4346 E Elwood Street - Suite 100, Phoenix, Arizona  85040
O: 602-272-2200 | M: 602-909-0678 | D: 480-351-5009
Connect With Us Socially 
            


-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Wednesday, January 07, 2015 2:36 PM
To: [email protected]
Subject: RE: Pressure Relief Valve on Wet Pipe System

Interesting to those whom question "why" about everything- I did not wonder 
'why grids but not trees' until a few years ago. I was getting nowhere on my 
own brain power so I asked and was told that grids have a trapped secondary 
main with aux drain and that helps get the air out so you do not have the air 
cushion like you do in a tree. Was the change made because of the increase in 
concern for getting the air out of both configurations these days?

Brad  

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Wednesday, January 07, 2015 2:13 PM
To: [email protected]
Subject: RE: Pressure Relief Valve on Wet Pipe System

Change to mandatory relief valve was in 2010.   

SL



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Aaron Peck
Sent: Wednesday, January 07, 2015 3:46 AM
To: [email protected]
Subject: Pressure Relief Valve on Wet Pipe System

I wonder if I've been doing it wrong all along since 2010, but NFPA 13,
2013 Ed. 7.1.2.1 require a pressure relief valve on ALL wet pipe sprinkler 
systems? I can't tell you how many times in the past none have been installed. 
Granted they might not have been all designed according to 2010+, but just 
surprised this hasn't jumped out at me before.

 

Looking back the 2007 code mentions only in "gridded wet pipe systems"
then
2010 eliminates the word "gridded" as well as the 2013 code reads the same as 
2010. What's strange is my 2010 Hand book doesn't denote that as a changed 
section, actually none show up. Does the Hand book remove those that are there 
in the standard version?

 

Well I learned something knew.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to