Brad,
In response to your question "why".
Yes, the relief valves were first required on only the gridded systems due to 
the lack of trapped air in the systems.
As an insurance inspector in the summertime here in Texas around the 
mid-1980's, we started to find existing gridded systems that were leaking. 
Several systems were noted with riser gauge pressure exceeding 200-psi which 
appeared to be causing the leaks. At first we thought that possibly this was 
from water hammer created by water trucks filling up from nearby hydrants and 
maybe closing the hydrant too quickly...so we had 24-hour pressure recorders 
installed at the risers. The recorders indicated that the pressure rise 
corresponded with the rise in temperature during the hot summer days, and all 
these systems were located in unconditioned warehouses with exposed metal deck 
roof systems. We did not notice the pressure rise on gridded systems in air 
conditioned buildings.
Sometime in the 1980's, the Texas State Board of Insurance published it's rules 
to require a small pressure relief valve on all gridded wet-pipe systems 
because they did not want to limit it to only unconditioned warehouses...and 
later this was submitted as a proposal to NFPA-13. 
I'm not a thermal engineer so I don't know why or how the air and the gridded 
systems were affected by the heat, but these are my recollections of why this 
was done.
rick  
On Wednesday, January 7, 2015 3:35 PM, Brad Casterline 
<[email protected]> wrote:
  


Interesting to those whom question "why" about everything- I did not wonder
'why grids
 but not trees' until a few years ago. I was getting nowhere on my
own brain power so I asked and was told that grids have a trapped secondary
main with aux drain and that helps get the air out so you do not have the
air cushion like you do in a tree. Was the change made because of the
increase in concern for getting the air out of both configurations these
days?

Brad  

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Wednesday, January 07, 2015 2:13 PM
To: [email protected]
Subject: RE: Pressure Relief Valve on Wet Pipe System

Change to mandatory relief valve was in 2010.  

SL



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Aaron Peck
Sent: Wednesday, January 07, 2015 3:46 AM
To: [email protected]
Subject: Pressure Relief Valve on Wet Pipe System

I wonder if I've been doing it wrong all along since 2010, but NFPA 13,
2013 Ed. 7.1.2.1 require a pressure relief valve on ALL wet pipe
sprinkler systems? I can't tell you how many times in the past none have
been installed. Granted they might not have been all designed according
to 2010+, but just surprised this hasn't jumped out at me before.



Looking back the 2007 code mentions only in "gridded wet pipe systems"
then
2010 eliminates the word "gridded" as well as the 2013 code reads the
same as 2010. What's strange is my 2010 Hand book doesn't denote that as
a changed section, actually none show up. Does the Hand book remove
those that are there in the standard version?



Well I learned something knew.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler

.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to