New addition in 2010. Historically they have been required on gridded wet pipe 
systems and downstream of pressure regulating valves.
They are actually simple to install and most times do not require draining the 
entire sprinkler system. There are 1/2" plugged ports on most 
TestanDrain/Inspector Test that first can be used to perform the 200lb hydro 
test then are also the same location to install a pressure relief valve. I 
don't want to violate forum rules mentioning a specific company but there is a 
video on one MFG site explaining the simple andquick installation.



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Aaron Peck
Sent: Wednesday, January 07, 2015 6:46 AM
To: [email protected]
Subject: Pressure Relief Valve on Wet Pipe System

I wonder if I've been doing it wrong all along since 2010, but NFPA 13, 2013 
Ed. 7.1.2.1 require a pressure relief valve on ALL wet pipe sprinkler systems? 
I can't tell you how many times in the past none have been installed. Granted 
they might not have been all designed according to 2010+, but just surprised 
this hasn't jumped out at me before.

 

Looking back the 2007 code mentions only in "gridded wet pipe systems" then
2010 eliminates the word "gridded" as well as the 2013 code reads the same as 
2010. What's strange is my 2010 Hand book doesn't denote that as a changed 
section, actually none show up. Does the Hand book remove those that are there 
in the standard version?

 

Well I learned something knew.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to