Not permitted. There was a proposal submitted on the last cycle to allow this, 
but it was rejected.


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Art Tiroly
Sent: Friday, February 6, 2015 3:29 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

I am having an argument with a contractor that is removing heads and drops then 
moving them to a new position. Sprinklers are QR less than 5 years old.
He is not removing the head from the drop or the 1x1/2 RC. He says he is not 
reusing sprinklers just relocating them with the drop nipple. He says this is 
standard practice. 
Does this violate 6.2.1.1? Do not reuse sprinklers removed from the system.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell