6.2.1.1 (2013) When a sprinkler has been removed for any reason, it shall not be reinstalled.
Duane Johnson Strickland Fire Protection -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Richard Carr Sent: Friday, February 6, 2015 3:38 PM To: [email protected] Subject: RE: Relocate sprinklers with drops If he is not pulling the head how is it a violation of NFPA? Richard Carr, SET Branch Manager Cox Fire Protection, Inc 6555 Grace Lane. Jacksonville, Fl. 32205 [email protected] 904-781-8227 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Duane Johnson Sent: Friday, February 06, 2015 3:29 PM To: [email protected] Subject: RE: Relocate sprinklers with drops The problem is, you won't find this in the standard unless you print out the ROC... Duane Johnson Strickland Fire Protection -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Duane Johnson Sent: Friday, February 6, 2015 3:28 PM To: [email protected] Subject: RE: Relocate sprinklers with drops Not permitted. There was a proposal submitted on the last cycle to allow this, but it was rejected. Duane Johnson Strickland Fire Protection -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Art Tiroly Sent: Friday, February 6, 2015 3:29 PM To: [email protected] Subject: RE: Relocate sprinklers with drops I am having an argument with a contractor that is removing heads and drops then moving them to a new position. Sprinklers are QR less than 5 years old. He is not removing the head from the drop or the 1x1/2 RC. He says he is not reusing sprinklers just relocating them with the drop nipple. He says this is standard practice. Does this violate 6.2.1.1? Do not reuse sprinklers removed from the system. Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org