Based on the 2nd draft, this is what the 2016 language will say unless it is 
Successfully NITMAM ed

6.2.1.1*  
When a sprinkler is removed from a fitting or welded outlet, it shall not be 
reinstalled except as permitted by 6.2.1.1.1.
6.2.1.1.1  
Dry sprinklers shall be permitted to be reinstalled when removed in accordance 
with the manufacturer's installation and maintenance instructions.

A.6.2.1.1  
Sprinklers should be permitted to be reinstalled when the sprinkler being 
removed from the system remains attached to the original fitting or welded 
outlet, provided care has been taken to ensure the sprinkler has not been 
damaged. Flexible hose connections are considered a fitting.
In new installations, where sprinklers are installed on pendent drop nipples or 
sidewall sprinklers prior to final cut-back, protective caps and/or straps 
should remain in place until after the drop nipple has been cut to fit to the 
final ceiling elevation.

This is my opinion only and does not constitute the official opinion of the 
NFPA.

Peter Schwab
VP of Purchasing & Engineering Technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com


 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of michael G
Sent: Friday, February 06, 2015 3:56 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

I would have to agree with Richard,  He is not pulling the head out of the 
piping, the Boss of the sprinkler is taking no extra strain and there is no 
extra stress added on the sprinkler head its self.  Only the piping is being 
removed, cut threaded and reinstalled.  We basically do this when we install a 
system....

We run the branch line, install a 0-2 and elbow, the drop and a head with the 
support ring installed already, so that when we do our initial testing for 
leaks, the drops are tested all the way to the sprinkler head. The reason for 
this is, 1) to eliminate the number of potential leaks at the end of the job 
while conducting the final pressure test. 2) if there is a bad head or 
something wrong, i.e.  cracked 1 x 1/2" RC, it is easier to change it out then, 
instead of over finished floor and product.


Mike 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Duane Johnson
Sent: Friday, February 06, 2015 3:44 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

6.2.1.1 (2013) When a sprinkler has been removed for any reason, it shall not 
be reinstalled.


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Richard Carr
Sent: Friday, February 6, 2015 3:38 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

If he is not pulling the head how is it a violation of NFPA?

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]
904-781-8227


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Duane Johnson
Sent: Friday, February 06, 2015 3:29 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

The problem is, you won't find this in the standard unless you print out the 
ROC...


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Duane Johnson
Sent: Friday, February 6, 2015 3:28 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

Not permitted. There was a proposal submitted on the last cycle to allow this, 
but it was rejected.


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Art Tiroly
Sent: Friday, February 6, 2015 3:29 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

I am having an argument with a contractor that is removing heads and drops then 
moving them to a new position. Sprinklers are QR less than 5 years old.
He is not removing the head from the drop or the 1x1/2 RC. He says he is not 
reusing sprinklers just relocating them with the drop nipple. He says this is 
standard practice. 
Does this violate 6.2.1.1? Do not reuse sprinklers removed from the system.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to