I would have to agree with Richard,  He is not pulling the head out of the
piping, the Boss of the sprinkler is taking no extra strain and there is no
extra stress added on the sprinkler head its self.  Only the piping is being
removed, cut threaded and reinstalled.  We basically do this when we install
a system....

We run the branch line, install a 0-2 and elbow, the drop and a head with
the support ring installed already, so that when we do our initial testing
for leaks, the drops are tested all the way to the sprinkler head. The
reason for this is, 1) to eliminate the number of potential leaks at the end
of the job while conducting the final pressure test. 2) if there is a bad
head or something wrong, i.e.  cracked 1 x 1/2" RC, it is easier to change
it out then, instead of over finished floor and product.


Mike 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Duane Johnson
Sent: Friday, February 06, 2015 3:44 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

6.2.1.1 (2013) When a sprinkler has been removed for any reason, it shall
not be reinstalled.


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Richard Carr
Sent: Friday, February 6, 2015 3:38 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

If he is not pulling the head how is it a violation of NFPA?

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]
904-781-8227


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Duane Johnson
Sent: Friday, February 06, 2015 3:29 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

The problem is, you won't find this in the standard unless you print out the
ROC...


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Duane Johnson
Sent: Friday, February 6, 2015 3:28 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

Not permitted. There was a proposal submitted on the last cycle to allow
this, but it was rejected.


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Art Tiroly
Sent: Friday, February 6, 2015 3:29 PM
To: [email protected]
Subject: RE: Relocate sprinklers with drops

I am having an argument with a contractor that is removing heads and drops
then moving them to a new position. Sprinklers are QR less than 5 years old.
He is not removing the head from the drop or the 1x1/2 RC. He says he is not
reusing sprinklers just relocating them with the drop nipple. He says this
is standard practice. 
Does this violate 6.2.1.1? Do not reuse sprinklers removed from the system.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________