Yeah NFPA uses multiple terms like System, Operating and Working pressure.   
Pick one.

But you're right Vince.  If one head opened and the pump came on the system's 
conditions probably could be close to the pump churn pressure.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Vince Sabolik
Sent: Tuesday, March 10, 2015 2:03 PM
To: [email protected]
Subject: Re: Pump you up?

NFPA Definition:

"3.3.23 System Working Pressure. The maximum anticipated static (nonflowing) or 
flowing pressure applied to sprinkler system components exclusive of surge 
pressures and exclusive of pressure from the fire department connection."


The pump's gonna start with one head and it will be very close to a churn 
pressure - say in excess of 175 psi.  So what would apply?
Operating pressure with "X" amount of heads flowing or the one head that 
started the fire pump?


On 3/10/2015 1:54 PM, [email protected] wrote:
> There's a difference between OPERATING pressure and SYSTEM pressure.
>
> Operating pressure would be the fire pump running and sprinklers operating.  
> Churn wouldn't play into this scenario.
>
> System pressure would be the pressure under static conditions with no flow.  
> So the shut off set pint of the jockey pump should be the upper limit.
>
> For Churn you usually shut off the line serving the sprinkler system so the 
> system downstream shouldn't see the churn pressure, right?
>
> Craig L. Prahl
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Vince Sabolik
> Sent: Tuesday, March 10, 2015 1:42 PM
> To: [email protected]
> Subject: Re: Pump you up?
>
> Unless somebody messes with the limit switch, the jockey pump will be "off " 
> on its own, no?
>
>
>
> On 3/10/2015 1:29 PM, John Denhardt wrote:
>> Tim - Please provide a reference for that information.
>> FYI - NFPA 20 Annex states Jockey Pump "off" setting as minimum static plus 
>> churn pressure of the fire pump.
>>
>> John
>>
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]] On Behalf Of 
>> Tim Stone
>> Sent: Tuesday, March 10, 2015 12:36 PM
>> To: [email protected]
>> Subject: RE: Pump you up?
>>
>> Don't forget to add about 10 PSI for the Jockey Pump.
>> City Static + Pump Churn + Jockey Pump 10 PSI =
>>
>>
>>
>> Regards,
>> G. Tim Stone
>>
>> G. Tim Stone Consulting, LLC
>> NICET Level III Engineering Technician Fire Protection Sprinkler 
>> Design and Consulting Services
>>
>>                   117 Old Stage Rd. - Essex Jct., VT. 05452
>> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>>                              [email protected]
>>
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]]
>> On Behalf Of John Denhardt
>> Sent: Tuesday, March 10, 2015 12:08 PM
>> To: <[email protected]>
>> Subject: Re: Pump you up?
>>
>> Maximum static plus churn would be my off the cuff answer.
>>
>> John
>>
>> Sprinklers Save
>>
>>> On Mar 10, 2015, at 11:55 AM, "Vince Sabolik" <[email protected]> wrote:
>>>
>>> Would a fire pump's churn pressure (city static + pump churn) 
>>> constitute the operating pressure of a sprinkler system?
>>>
>>> The red book has me confused.
>>>
>>> Again.
>>>
>>>
>>>                                              thanks, Vince
>>>
>>>
>>> West Tech Fire Protection, Inc.
>>> 11351 Pearl Road   / Strongsville, Ohio   44136
>>> Phone 440 238-4800    Fax 440 238-4876   Cell  440 724-7601
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> k
>>> l
>>> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>>
>>
>


-- 

West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800    Fax 440 238-4876   Cell  440 724-7601
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to