Tim - Please provide a reference for that information.
FYI - NFPA 20 Annex states Jockey Pump "off" setting as minimum static plus 
churn pressure of the fire pump.

John

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tim Stone
Sent: Tuesday, March 10, 2015 12:36 PM
To: [email protected]
Subject: RE: Pump you up?

Don't forget to add about 10 PSI for the Jockey Pump. 
City Static + Pump Churn + Jockey Pump 10 PSI =



Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Denhardt
Sent: Tuesday, March 10, 2015 12:08 PM
To: <[email protected]>
Subject: Re: Pump you up?

Maximum static plus churn would be my off the cuff answer.  

John

Sprinklers Save

> On Mar 10, 2015, at 11:55 AM, "Vince Sabolik" <[email protected]> wrote:
> 
> Would a fire pump's churn pressure (city static + pump churn) 
> constitute the operating pressure of a sprinkler system?
> 
> The red book has me confused.
> 
> Again.
> 
> 
>                                            thanks, Vince
> 
> 
> West Tech Fire Protection, Inc.
> 11351 Pearl Road   / Strongsville, Ohio   44136
> Phone 440 238-4800    Fax 440 238-4876   Cell  440 724-7601
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to