No beef. I'm presuming maximum pressure also refers to the water supply.
In that context, a temporary boost (as in a pump churn) would not
constitute working water pressure while discharge of one head that
turned the
pump on would, no?
Vince
On 3/12/2015 10:04 AM, Roland Huggins wrote:
Exactly what it says. It might help for you to look at where it is used in the
standard. It’s covers three items: the required pressure rating of components,
the required hydrostatic test, and the sizing of the expansion chamber. All of
these items are about maximum pressure. So when the definition says the
maximum pressure whether when flowing or non-flowing where’s the beef?
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
On Mar 11, 2015, at 11:42 AM, Vince Sabolik <[email protected]> wrote:
On 3/11/2015 12:03 PM, Roland Huggins wrote:
The needed answer depends on what is the underlying or driving question in why
you ask
All right, define "working pressure".
Would that be the pressure available at no flow; pressure at design flow;
or the pressure present at one head flowing?
In the NFPA definitions, it says "the maximum anticipated static (nonflowing)
or flowing pressure"
Either or?
Who (or what) is supposed to determine?
West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org