The main point is that for standard high rises, the codes and standards only 
require a single riser.

Very Tall High Rises (>420 ft) are a unique beast.  The IFC requires these tall 
buildings to have 2 risers per zone.  Not 100% sure but I don’t think they mean 
each floor is a zone.  The same section says “Each riser shall supply 
sprinklers on alternate floors”.  A lot of these building going up in parts of 
the Middle East but not hearing about any here in the USA.  Any one involved 
with one?

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Mar 20, 2015, at 9:55 AM, David Blackwell <[email protected]> 
> wrote:
> 
> It is also found in Section 914.3.1.1 of the 2012 IFC, which is referenced 
> from 2012 IFC Table 903.2.11.6 [Additional Required Fire Suppression Systems].
> 
> Respectfully,
> 
> 
> David W. S. Blackwell, II, PE, CFPE, CFI I
> Chief Engineer
> Office of State Fire Marshal
> SC Department of Labor, Licensing, & Regulation, 141 Monticello Trail, 
> Columbia, SC 29203
> Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
> Fax: 803.896.9806 [Office]
> Email:   [email protected]
> Website:  http://www.scfiremarshal.llronline.com/
> 
> 
> Please note that you can sign up to receive automatic information on SC 
> Division of Fire and Life Safety current events, policies, laws and 
> procedures by visiting our Web site at:  
> http://www.scfiremarshal.llronline.com/
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Fairchild, Jack
> Sent: Friday, March 20, 2015 12:15 PM
> To: [email protected]
> Subject: RE: Floor Control Stations
> 
> IBC 2009/2012  -  403.3.1  Buildings in excess of 420 feet in height.
> 
> Jack Fairchild
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Dale Wingard
> Sent: Friday, March 20, 2015 11:45 AM
> To: '[email protected]'
> Subject: RE: Floor Control Stations
> 
> Jeremy,
> 
> I believe that is just a Marriott requirement.
> 
> Dale F. Wingard  SET
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Jeremy Frazier
> Sent: Friday, March 20, 2015 10:38 AM
> To: [email protected]
> Subject: Floor Control Stations
> 
> Where in NFPA/IBC does it say that if you have 2 standpipes, your sprinkler 
> system should connect to both standpipes?  I've looked through 14 (2010),13
> (2010) and IBC (2009)  and I have not found anything requiring it.  Is this 
> one of those things like electrical rooms with 2 penetrations or is there and 
> actual code?  
> 
> 
> 
> 
> 
> Jeremy Frazier
> 
> P:571-931-1004
> F:571-931-1010
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to