That is what I was concerned about.  So it looks like when you are dealing with 
pallet storage/floor storage of small plastic containers, it is outside the 
scope of NFPA?

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Morey, Mike
Sent: Friday, May 22, 2015 7:44 AM
To: [email protected]
Subject: Re: NFPA 30 - Class IIIB Plastic Containers

I would surmise based on the way the definition is laid out that an IBC would 
be between 119 and 793 gallons (since containers are 119 and under).  A quick 
google of the term suggests the plastic tank built into a pallet type container 
is what is commonly refereed to as an IBC.  Also a quick google of 
"Intermediate bulk container regulations" take you to an NFPA faq sheet that 
agrees with my assumption (you may need to google yourself as direct links via 
google to PDFs frequently don't work): 
http://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&ved=0CB4QFjAA&url=http%3A%2F%2Fwww.nfpa.org%2F~%2Fmedia%2Ffiles%2Fresearch%2Fresearch-foundation%2Fibc%2Ffact-sheets%2Fibc-faqsheet_update.pdf%3Fla%3Den&ei=bkBfVZ3fN8zutQXp_YCYDw&usg=AFQjCNHAqe8HiXSAVlC9SvDU5Bs1gywa5Q&sig2=rCppdasfz56bLuov0zagnw&bvm=bv.93990622,d.b2w&cad=rja

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
[email protected] | www.bmwc.com

________________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Gregg Fontes <[email protected]>
Sent: Friday, May 22, 2015 10:21 AM
To: [email protected]
Subject: NFPA 30 - Class IIIB Plastic Containers

Scenario, quarts, gallons, and 5 gallons plastic containers of a Class IIIB 
liquid (i.e. motor oil, gear oil, hydraulic oil) stored 5' high on pallets for 
shipment to typical retail automotive stores.  The quarts and gallon containers 
will be in cardboard boxes.  The 5 gallons will be stacked two high on a 
pallets.  First, would these containers be considered IBC's (intermediate bulk 
containers per 3.3.12.2 - 2015 edition)?  If so, then I assume Table 16.5.2.9 
would apply?  If not considered IBC's, what Table would apply, if any?

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________