Take a look at 12.8.1 (2012 ed don't have 15 handy). It looks like your scenario would be class IV density. You can have 13,750 gallons IIIB before chapter 16 kicks in.
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jeremy Frazier Sent: Friday, May 22, 2015 1:48 PM To: [email protected] Subject: RE: NFPA 30 - Class IIIB Plastic Containers What is the total quantities? Because unless there is a lot of them, you probably don't need to go that far in 30. Unprotected flammable liquids is ordinary grp 2. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Gregg Fontes Sent: Friday, May 22, 2015 10:22 AM To: [email protected] Subject: NFPA 30 - Class IIIB Plastic Containers Scenario, quarts, gallons, and 5 gallons plastic containers of a Class IIIB liquid (i.e. motor oil, gear oil, hydraulic oil) stored 5' high on pallets for shipment to typical retail automotive stores. The quarts and gallon containers will be in cardboard boxes. The 5 gallons will be stacked two high on a pallets. First, would these containers be considered IBC's (intermediate bulk containers per 3.3.12.2 - 2015 edition)? If so, then I assume Table 16.5.2.9 would apply? If not considered IBC's, what Table would apply, if any? Thanks, Gregg Fontes Cen-Cal Fire Systems, Inc. 209-334-9119 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org