I guess It all goes back to unprotected flammable liquids vs protected
flammable liquids.   It's unreasonable to expect every building with any
flammable liquids in it to have a foam system with a pump or a 8'-12' main
with 6000 sqft remote area.  If that were the case, all you really would
have is a bunch of places illegally storing flammable liquids/people just
not adopting it.  So they threw an ok density at it and limited the
amount/type of liquids you can store under the idea that the fire can only
be so bad.  If you want to store more, well then you need to do all this and
that so we don’t have an explosion leveling a few city blocks.   It is kind
of stupid that they say use class IV but oh by the way it might not work
(because that’s very helpful, especially in a court of law).  

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John F Hoffman
Sent: Friday, May 22, 2015 4:24 PM
To: [email protected]
Subject: RE: NFPA 30 - Class IIIB Plastic Containers

If you look at the annex material, fire control using the 12.8.1 protection
scheme may not be achieved.  Which makes you wonder how it came to be a
design option.   Something to consider.   All the chapter 16 options use the
schemes A,B, or C for plastic containers.

John F. Hoffman, PE*  \  Burns & McDonnell Senior Fire Protection Engineer O
816-349-6759 \  M 816-255-4102 [email protected]  \  burnsmcd.com
9400 Ward Parkway  \  Kansas City, MO 64114

Proud to be one of FORTUNE's 100 Best Companies to Work For Please consider
the environment before printing this email.
*Registered in: MO

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jeremy Frazier
Sent: Friday, May 22, 2015 12:59 PM
To: [email protected]
Subject: RE: NFPA 30 - Class IIIB Plastic Containers

Take a look at 12.8.1 (2012 ed don't have 15 handy).  It looks like your
scenario would be  class IV density.  You can have  13,750 gallons IIIB
before chapter 16 kicks in.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jeremy Frazier
Sent: Friday, May 22, 2015 1:48 PM
To: [email protected]
Subject: RE: NFPA 30 - Class IIIB Plastic Containers

What is the total quantities?  Because unless there is a lot of them, you
probably don't need to go that far in 30.  Unprotected flammable liquids is
ordinary grp 2.    

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Gregg Fontes
Sent: Friday, May 22, 2015 10:22 AM
To: [email protected]
Subject: NFPA 30 - Class IIIB Plastic Containers

Scenario, quarts, gallons, and 5 gallons plastic containers of a Class IIIB
liquid (i.e. motor oil, gear oil, hydraulic oil) stored 5' high on pallets
for shipment to typical retail automotive stores.  The quarts and gallon
containers will be in cardboard boxes.  The 5 gallons will be stacked two
high on a pallets.  First, would these containers be considered IBC's
(intermediate bulk containers per 3.3.12.2 - 2015 edition)?  If so, then I
assume Table 16.5.2.9 would apply?  If not considered IBC's, what Table
would apply, if any?      

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com