If you look at the annex material, fire control using the 12.8.1 protection 
scheme may not be achieved.  Which makes you wonder how it came to be a design 
option.   Something to consider.   All the chapter 16 options use the schemes 
A,B, or C for plastic containers.

John F. Hoffman, PE*  \  Burns & McDonnell
Senior Fire Protection Engineer
O 816-349-6759 \  M 816-255-4102 
[email protected]  \  burnsmcd.com
9400 Ward Parkway  \  Kansas City, MO 64114

Proud to be one of FORTUNE's 100 Best Companies to Work For
Please consider the environment before printing this email.
*Registered in: MO

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jeremy Frazier
Sent: Friday, May 22, 2015 12:59 PM
To: [email protected]
Subject: RE: NFPA 30 - Class IIIB Plastic Containers

Take a look at 12.8.1 (2012 ed don't have 15 handy).  It looks like your 
scenario would be  class IV density.  You can have  13,750 gallons IIIB before 
chapter 16 kicks in.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jeremy Frazier
Sent: Friday, May 22, 2015 1:48 PM
To: [email protected]
Subject: RE: NFPA 30 - Class IIIB Plastic Containers

What is the total quantities?  Because unless there is a lot of them, you 
probably don't need to go that far in 30.  Unprotected flammable liquids is
ordinary grp 2.    

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Gregg Fontes
Sent: Friday, May 22, 2015 10:22 AM
To: [email protected]
Subject: NFPA 30 - Class IIIB Plastic Containers

Scenario, quarts, gallons, and 5 gallons plastic containers of a Class IIIB 
liquid (i.e. motor oil, gear oil, hydraulic oil) stored 5' high on pallets for 
shipment to typical retail automotive stores.  The quarts and gallon containers 
will be in cardboard boxes.  The 5 gallons will be stacked two high on a 
pallets.  First, would these containers be considered IBC's (intermediate bulk 
containers per 3.3.12.2 - 2015 edition)?  If so, then I assume Table 16.5.2.9 
would apply?  If not considered IBC's, what Table
would apply, if any?      

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to