What edition?  What standpipe class?

Assuming fairly recent edition and Class I manual dry:
Two remote hose stations at 250 gpm for 500 gpm at remote standpipe
250 for each additional standpipe to a total of 1000 gpm for sprinklered building, or 1250 for unsprinklered building.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 8/12/2015 11:28 AM, Steve Leyton wrote:
Also prudent to ask, which edition of NFPA 14 is being applied?


SL




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Cliff Whitfield
Sent: Wednesday, August 12, 2015 11:27 AM
To: [email protected]
Subject: RE: ...so a standpipe walks into a bar...

Vince,

Is the building fully/completely sprinklered?

Cliff

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Vince Sabolik
Sent: Wednesday, August 12, 2015 12:21 PM
To: [email protected]
Subject: ...so a standpipe walks into a bar...

Hello Forum --

I have a building with a dry, manual standpipe fed from an FDC.

There are six standpipes with 2½" valves.

Can someone break down the NFPA flow requirement, Barney-style for me?

I'm thinking 500 gpm first and 250 gpm each additional. My question is how many 
additional?

I guess they should put more pictures in the code!


thanks, Vince

West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800    Fax 440 238-4876   Cell  440 724-7601
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to