Oh..I thought he meant 90k sq ft per floor.

Would be hard to get 6 standpipes in what I assume is minimum 4 story building. That would be 22.5k sq ft per floor. I can't see having 6 standpipes on a floor area that small...but it is possible.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 8/12/2015 11:58 AM, Cliff Whitfield wrote:
Travis,

His building is 90k total, not per floor.  I don't think what you just posted 
applies.

Cliff

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Wednesday, August 12, 2015 12:54 PM
To: [email protected]
Subject: Re: ...so a standpipe walks into a bar...

90k sq ft changes things...
For buildings over 80k sq ft, you do 500+500+250

*7.10.1.1.3 *The minimum flow rate for additional standpipes shall be 250 gpm 
(946 L/min) per standpipe for buildings with floor areas that do not exceed 
80,000 ft2 (7432 m2) per floor. For buildings that exceed 80,000 ft2 (7432 m2) 
per floor, the minimum flow rate for the additional standpipes shall be
500 gpm (1893 L/min) for the second standpipe and 250 gpm
(946 L/min) for the third standpipe if the additional flow is required for an 
unsprinklered building.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 8/12/2015 11:53 AM, Vince Sabolik wrote:
I really don't know if it should be I or III. No sprinklers and - oh, 90,000 sq 
ft. Current code. I'm thinking 500 + 250 until 1,250 but I can't see that in 14 
anymore. Old age setting in again? Thanks for the help.

On Aug 12, 2015, Vince Sabolik <[email protected]> wrote:

Hello Forum --

I have a building with a dry, manual standpipe fed from an FDC.

There are six standpipes with 2½" valves.

Can someone break down the NFPA flow requirement, Barney-style for me?

I'm thinking 500 gpm first and 250 gpm each additional. My question is
how many additional?

I guess they should put more pictures in the code!


thanks, Vince

West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio 44136 Phone 440 238-4800 Fax 440
238-4876 Cell 440 724-7601
_____________________________________________

Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org


- Somehow, this made it through Verizon Wireless and got to you!
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to