You're right.  I guess Vince will have to let us know.

Cliff

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Wednesday, August 12, 2015 1:02 PM
To: [email protected]
Subject: Re: ...so a standpipe walks into a bar...

Oh..I thought he meant 90k sq ft per floor.

Would be hard to get 6 standpipes in what I assume is minimum 4 story building. 
 That would be 22.5k sq ft per floor.  I can't see having 6 standpipes on a 
floor area that small...but it is possible.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 8/12/2015 11:58 AM, Cliff Whitfield wrote:
> Travis,
>
> His building is 90k total, not per floor.  I don't think what you just posted 
> applies.
>
> Cliff
>
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Travis Mack, SET
> Sent: Wednesday, August 12, 2015 12:54 PM
> To: [email protected]
> Subject: Re: ...so a standpipe walks into a bar...
>
> 90k sq ft changes things...
> For buildings over 80k sq ft, you do 500+500+250
>
> *7.10.1.1.3 *The minimum flow rate for additional standpipes shall be 
> 250 gpm (946 L/min) per standpipe for buildings with floor areas that 
> do not exceed 80,000 ft2 (7432 m2) per floor. For buildings that 
> exceed 80,000 ft2 (7432 m2) per floor, the minimum flow rate for the 
> additional standpipes shall be
> 500 gpm (1893 L/min) for the second standpipe and 250 gpm
> (946 L/min) for the third standpipe if the additional flow is required for an 
> unsprinklered building.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 8/12/2015 11:53 AM, Vince Sabolik wrote:
>> I really don't know if it should be I or III. No sprinklers and - oh, 90,000 
>> sq ft. Current code. I'm thinking 500 + 250 until 1,250 but I can't see that 
>> in 14 anymore. Old age setting in again? Thanks for the help.
>>
>> On Aug 12, 2015, Vince Sabolik <[email protected]> wrote:
>>
>> Hello Forum --
>>
>> I have a building with a dry, manual standpipe fed from an FDC.
>>
>> There are six standpipes with 2½" valves.
>>
>> Can someone break down the NFPA flow requirement, Barney-style for me?
>>
>> I'm thinking 500 gpm first and 250 gpm each additional. My question 
>> is how many additional?
>>
>> I guess they should put more pictures in the code!
>>
>>
>> thanks, Vince
>>
>> West Tech Fire Protection, Inc.
>> 11351 Pearl Road / Strongsville, Ohio 44136 Phone 440 238-4800 Fax 
>> 440
>> 238-4876 Cell 440 724-7601
>> _____________________________________________
>>
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>>
>>
>> - Somehow, this made it through Verizon Wireless and got to you!
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to