I guess I was taught right. I've always done the most demanding area. I
see that
there could be confusion - say on a design program that picks the most
remote heads.
Good point!
On 8/12/2015 5:34 PM, rongreenman . wrote:
Vince,
"Hydraulically most remote" and "hydraulically most demanding" are to
separate things. The former may be the latter but not necessarily. Nice
warm S2 parking garage, ground floor mercantile, two floors above that of
apartments. All on the same system. Hydraulically most remote will be at
the top. Hydraulically most demanding could very well be at ground level,
or maybe even the parking garage.
On Wed, Aug 12, 2015 at 1:44 PM, Vince Sabolik <[email protected]> wrote:
To all - even Ron in the hole.
Don't they use the words "hydraulically most remote" any more?
AND thanks for coming through for me Forum!
On 8/12/2015 4:29 PM, rongreenman . wrote:
Travis, not a shot at you per se but you gave me an opportunity to vent. I
think we, as an industry, and those of us that play here especially, need
to stop saying remote to mean hydraulically most demanding. In the days
when sprinklered buildings were pretty much exclusively open floor
factories and warehouses and we were using the pipe schedule remote
location for inspectors test ports made sense. Even when we went to early
hydraulics in the same types of buildings, but now with places that have
more demanding stuff in the middle or multiple design areas I think
"remote" confuses the new guys. I'd just like the language changed. A pet
peeve. Off my box and back in my hole. Thank you for your support. Ed
Jaymes.
On Wed, Aug 12, 2015 at 12:07 PM, Travis Mack, SET <[email protected]>
wrote:
West Tech Fire Protection, Inc.
11351 Pearl Road
Suite 102
Strongsville, Ohio 44136
T 440 238-4800 F 440 238-4876C 440 724-7601
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
West Tech Fire Protection, Inc.
11351 Pearl Road
Suite 102
Strongsville, Ohio 44136
T 440 238-4800 F 440 238-4876C 440 724-7601
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org