Your self-storage building feature a hallway-cloud design with financially
inconvenient prescriptive sprinkler implications.

What about the "width" as measured n the direction parallel with the
hallway?  The obstruction length in that direction exceeds 4 feet.   Though
stored goods in quantity should not be in the hallway for substantial
amounts of time, and if a fire were to occur in
hallway-located-combustibles, the fire likely would not advance into the
storage rooms (liquid fuels being the exception, but even then there are
sprinklers in the storage rooms).  If I were writing the specification for
bid on this project, I would have declared that sprinklers cover the
60-inich wide hallway at the lower cloud level before they covered the
hallway at the obstructed ceiling level.


Scot Deal
Excelsior Fire/Risk Engineering