It would be more of a cloud type ceiling.  Yes.  

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of IPA
Sent: Thursday, August 20, 2015 3:59 PM
To: [email protected]
Subject: Re: Obstruction

Do you mean a cloud ceiling rather than a 'soffit?'


On Wed, Aug 19, 2015 at 8:06 PM, AKS-Gmail-IMAP <[email protected]> wrote:

> This is a trick question, right? The hallway width should be at least 
> as wide as the code minimum width for persons on foot plus the width 
> of whatever the maximum size the storage room doors are because that 
> would be the width of items that could normally be expected to be in 
> the hallway during dire egress conditions. So if the bare bones public 
> hallway minimum width is 44 inches then the doors to the storage rooms 
> must be for golf club bags only. This sounds like an attempt to skirt 
> the sprinkler standard intent in a building that is also skirts the building 
> code intent.
>
> Allan Seidel
> St. Louis, MO
>
>
> > On Aug 19, 2015, at 11:29 AM, Gregg Fontes <[email protected]>
> wrote:
> >
> > Any opinions/thoughts?
> >
> > Looking at a typical mini storage facility.  At the 5' wide hallways
> (walls full height to concrete deck) they are looking to install a 3' 
> wide soffit/ceiling down the middle of the hallway.  This will leave a 
> 1' gap on each side of the hallway.  The soffit/ceiling will be approximately 
> 24"
> below the upright fire sprinkler deflector that is running down the 
> center of the hallway.  Since the soffit/ceiling (continuous 
> obstruction) is less than 4' wide and greater than 18" below the fire 
> sprinkler deflector, then am I correct in thinking that fire 
> sprinklers are not required per NFPA 13
> 2013 8.5.5.3 to be installed at the soffit/ceiling?
> >
> > Thanks,
> > Gregg Fontes
> > Cen-Cal Fire Systems, Inc.
> > 209-334-9119
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to