Look into CWSI if you have to add them

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Drucker
Sent: Monday, August 31, 2015 10:15 PM
To: [email protected]
Subject: Re: AHJ Powers

Then typically unless you have a written variation approval (citing the code 
requirement, why compliance could not be achieved, and what equivalent measures 
where taken) a code violation exists. Aside from all that the only sleepless 
nights will occur when another code Official cites it years later or when you 
get to visit a room that resembles a church but isn't but you still swear to 
god.

John Drucker - Mobile Email
Asst Construction Official
Fire Protection Subcode Official
[email protected]<mailto:[email protected]>
Cell/Text 732-904-6823


[email protected] wrote:

Yes

Sent from my iPhone

> On Aug 31, 2015, at 6:14 PM, John Drucker <[email protected]> wrote:
>
> Are the valves required to be electrically supervised by applicable code ?
>
> John Drucker - Mobile Email
> Asst Construction Official
> Fire Protection Subcode Official
> [email protected]<mailto:[email protected]>
> Cell/Text 732-904-6823
>
>
> [email protected] wrote:
>
> What say you?
> An inspector failed to require tamper switches on control valves. The job is 
> complete and there are thousands of pounds of concrete between the control 
> valves and the electrical panel. They placed a chain and lock and the chief 
> declared the chain and lock meet intent...final approved. What say you?
>
> Sent from my iPhone
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to