Yeah this is where the NFPA people need to be in-line with the ICC people.    
But the ICC also makes no exceptions for those installations where there is no 
alarm system to connect any signals.

Keep the documentation of the AHJ approval for posterity.  He signed off, he's 
the final say.  Move on to the next great adventure.

Round and round the mulberry bush.....................................


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Tuesday, September 01, 2015 8:15 AM
To: [email protected]
Subject: RE: AHJ Powers

If the system is a Required system per IBC, then valves controlling water to 
sprinklers must be electrically supervised.

It is an IBC violation, not NFPA if I am assuming correctly.

R/
Matt

Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
1805 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Cell-605.391.2733
Fax:-605.348.0108



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, September 01, 2015 6:12 AM
To: [email protected]
Subject: RE: AHJ Powers

NFPA 13 gives clear options, chaining and locking is one of them.  What's the 
issue here?  There are building installations where there is no requirement for 
a fire alarm system so there is no provision for supervising valves 
electronically, in those cases you chain or lock them.

8.16.1.1.2* Supervision.
8.16.1.1.2.1 Valves on connections to water supplies, sectional control and 
isolation valves, and other valves in supply pipes to sprinklers and other 
fixed water-based fire suppression systems shall be supervised by one of the 
following methods:
(1) Central station, proprietary, or remote station signaling service
(2) Local signaling service that will cause the sounding of an audible signal 
at a constantly attended point
(3) Valves locked in the correct position
(4) Valves located within fenced enclosures under the control of the owner, 
sealed in the open position, and inspected weekly as part of an approved 
procedure




Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, August 31, 2015 8:49 PM
To: [email protected]
Subject: AHJ Powers

What say you?
An inspector failed to require tamper switches on control valves. The job is 
complete and there are thousands of pounds of concrete between the control 
valves and the electrical panel. They placed a chain and lock and the chief 
declared the chain and lock meet intent...final approved. What say you?

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to