NFPA 13 gives clear options, chaining and locking is one of them.  What's the 
issue here?  There are building installations where there is no requirement for 
a fire alarm system so there is no provision for supervising valves 
electronically, in those cases you chain or lock them.

8.16.1.1.2* Supervision.
8.16.1.1.2.1 Valves on connections to water supplies, sectional
control and isolation valves, and other valves in supply pipes to
sprinklers and other fixed water-based fire suppression systems
shall be supervised by one of the following methods:
(1) Central station, proprietary, or remote station signaling service
(2) Local signaling service that will cause the sounding of an audible signal 
at a constantly attended point
(3) Valves locked in the correct position
(4) Valves located within fenced enclosures under the control of the owner, 
sealed in the open position, and inspected weekly as part of an approved 
procedure




Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, August 31, 2015 8:49 PM
To: [email protected]
Subject: AHJ Powers

What say you?
An inspector failed to require tamper switches on control valves. The job is 
complete and there are thousands of pounds of concrete between the control 
valves and the electrical panel. They placed a chain and lock and the chief 
declared the chain and lock meet intent...final approved. What say you?

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to