Regarding AHJ code interpretation issues, my experience is that an informal 
interpretation from NFPA will resolve almost all issues. They can be obtained 
fairly quickly by contacting NFPA. The only exception would be where the local 
AHJ has specific requirements over and above NFPA code. 

  




Bill Menster 
WFM Consulting Inc. 
2416 Malaya Ct. 
Punta Gorda, FL 33983 
ph. 941-421-9786 
fax 941-391-6133 
[email protected] 
www.wfmconsultinginc.com 


----- Original Message -----

From: "Greg McGahan" <[email protected]> 
To: "sprinklerforum" <[email protected]> 
Sent: Tuesday, November 10, 2015 3:24:16 PM 
Subject: Re: Quick Response Reduction 

He is incorrect unless the ceiling is open enough to count the roof deck as 
part of the same space. The table states "ceiling height". 

Respectfully, 



Greg McGahan 
Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 
1160 McKenzie Road 
Cantonment, FL 32533 
850-937-1850 
fax 850-937-1852 

On Tue, Nov 10, 2015 at 2:19 PM, Rocci Cetani 3 <[email protected]> 
wrote: 

> I have an AHJ claiming that because the roof deck is 18' I can't use the 
> 40% 
> quick response reduction even though a ceiling is being installed at 9' 
> AFF. 
> I have never been questioned on my approach it seems pretty straight 
> forward..Is he correct in stating I should base my reduction on the 18' 
> roof 
> deck? 
> 
> 
> 
> Thanks in advance for your input 
> 
> 
> 
> Rocci Cetani III, CET 
> 
> Lead Designer 
> 
> Water-Based Fire Protections Systems Layout, Nicet Level III 
> 
> 
> 
> Northern California Fire Protection Services Inc. 
> 
> 16840 Joleen Way Bldg. A 
> 
> Morgan Hill, CA 93037 
> 
> P-(408) 776-1580 EXT.111 
> 
> F-(408) 776-1590 
> 
> 
> 
> 
> 
> [email protected] 
> 
> www.norcalfire.com <http://www.norcalfire.com/> 
> 
> 
> 
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
> contain confidential information 
> 
> belonging to the sender. The information is intended only for the use of 
> individual or entity named above. If you are not the intended recipient, or 
> the employee or agent responsible to deliver this message to the intended 
> recipient, you are hereby notified that any disclosure, copying or taking 
> of 
> any action in reliance on the contents of this information is strictly 
> prohibited. If you have received this transmission in error, please 
> immediately notify us by telephone to arrange for return of the documents. 
> 
> 
> 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to