No it is light hazard and this was his response after I argued the
point..... "The most demanding design area is not the T-Bar ceiling, but the
attic.   The Code States "the system area of operation shall be permitted."
So the system area of operation is the attic at 18'.  You can reduce to 18',
but not to 10'. " 

 

That being said  I calculated the attic  because its sloped so the design
area needed to be increased 30% so I did that and then proceeded to reduce
it 40% because the attic at its peak is 9' above tee bar...   

 

Rocci Cetani III, CET

Lead Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected]

www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Gary Stites
Sent: Tuesday, November 10, 2015 3:15 PM
To: [email protected]
Subject: Re: Quick Response Reduction

 

Also, just a "heads-up" but in California you can only take that reduction
for Light Hazard...is that what he's thinking possibly?

 

Gary

 

On Tue, Nov 10, 2015 at 2:04 PM, Roland Huggins <
<mailto:[email protected]> [email protected]>

wrote:

 

> with the understanding that it is available only if you are an NFPA 

> member

> - just like AFSA informal interpretations.

> 

> Roland

> 

> 

> Roland Huggins, PE - VP Engineering

> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives

> Dallas, TX

>  <http://www.firesprinkler.org> http://www.firesprinkler.org <
<http://www.firesprinkler.org/> http://www.firesprinkler.org/>

> 

> 

> 

> 

> 

> > On Nov 10, 2015, at 1:11 PM,  <mailto:[email protected]>
[email protected] wrote:

> >

> > Regarding AHJ code interpretation issues, my experience is that an

> informal interpretation from NFPA will resolve almost all issues. They 

> can be obtained fairly quickly by contacting NFPA. The only exception 

> would be where the local AHJ has specific requirements over and above NFPA
code.

> >

> >

> >

> >

> >

> >

> > Bill Menster

> > WFM Consulting Inc.

> 

> _______________________________________________

> Sprinklerforum mailing list

>  <mailto:[email protected]>
[email protected]

> 

>  <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl

> er.org

> 

 

 

 

--

Gary Stites

*805-769-GMAN*

 

RLH < <http://www.rlhfp.com> http://www.rlhfp.com>

 <http://WWW.K25.Rocks> WWW.K25.Rocks

Pandora Station < <http://www.pandora.com/?sc=sh43464983213902734>
http://www.pandora.com/?sc=sh43464983213902734>

_______________________________________________

Sprinklerforum mailing list

 <mailto:[email protected]>
[email protected]

 
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to