Mr. Bilbo:
Our esteemed State Building Standards Commission has amended NFPA 13 to exclude
the quick response area reduction for ordinary hazard. We also have an
amendment that when a reduction is taken, the design area shall be 7 sprinklers
minimum and not 5.
Sincerely and spologetically,California
-------- Original message --------
From: Sprinkler Academy - C Bilbo <[email protected]>
Date: 11/10/2015 4:30 PM (GMT-08:00)
To: [email protected]
Subject: RE: Quick Response Reduction
Mr Stites,
You may care to review the four requirements for using the Quick Response
Reduction (Is that 11.2.3.2.3?) One of the "Design Advantage" strategies is to
use the QR Redux in Ordinary Hazard and this can significantly affect the cost
of a system. Yo.
It should be recognized that the above is my opinion as a member of the NFPA,
and has not been processed as a formal interpretation in accordance with the
NFPA Regulations Governing Committee Projects and should therefore not be
considered, nor relied upon, as the official position of the the NFPA, nor any
of their technical committees.
Sincerely,
Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com
[email protected]
OUR STUDENTS SAVE LIVES!!
> From: [email protected]
> Date: Tue, 10 Nov 2015 15:15:10 -0800
> Subject: Re: Quick Response Reduction
> To: [email protected]
>
> Also, just a "heads-up" but in California you can only take that reduction
> for Light Hazard...is that what he's thinking possibly?
>
> Gary
>
> On Tue, Nov 10, 2015 at 2:04 PM, Roland Huggins <[email protected]>
> wrote:
>
> > with the understanding that it is available only if you are an NFPA member
> > - just like AFSA informal interpretations.
> >
> > Roland
> >
> >
> > Roland Huggins, PE - VP Engineering
> > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
> > Dallas, TX
> > http://www.firesprinkler.org <http://www.firesprinkler.org/>
> >
> >
> >
> >
> >
> > > On Nov 10, 2015, at 1:11 PM, [email protected] wrote:
> > >
> > > Regarding AHJ code interpretation issues, my experience is that an
> > informal interpretation from NFPA will resolve almost all issues. They can
> > be obtained fairly quickly by contacting NFPA. The only exception would be
> > where the local AHJ has specific requirements over and above NFPA code.
> > >
> > >
> > >
> > >
> > >
> > >
> > > Bill Menster
> > > WFM Consulting Inc.
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Gary Stites
> *805-769-GMAN*
>
> RLH <http://www.rlhfp.com>
> WWW.K25.Rocks
> Pandora Station <http://www.pandora.com/?sc=sh43464983213902734>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org