The fact that they are listed, I reckon.
J. Scott Mitchell, PE
Fire Protection Engineer |
Projects Engineering
CNS Pantex | 806.477.5883 |
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Michael Hill
Sent: Tuesday, January 19, 2016 7:37 AM
To: [email protected]
Subject: RE: Ductile Iron Fittings
To expand on this a bit more. Most of the grooved fittings that are used are
ductile iron, what allows their use.
Mike Hill
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Michael Hill
Sent: Tuesday, January 19, 2016 8:27 AM
To: [email protected]
Subject: RE: Ductile Iron Fittings
How about working this from the other end. Get the listings for the proposed
fittings and seeing if any of them are acceptable in NFPA.
Mike Hill
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Monday, January 18, 2016 5:22 PM
To: [email protected]
Subject: RE: Ductile Iron Fittings
Yes, Chapter 10 gives the standards for DI pipe and fittings, but apparently
Chapter 10 isn't applicable to a riser manifold or spool piece.
6.3.1.1.1* Underground pipe shall be permitted to extend into the building
through the slab or wall not more than 24 in.
(600 mm).
10.1.4.1* Underground piping shall be permitted to extend into the building
through the slab or wall not more than 24 in.
(600 mm). [24:10.1.4.1]
This may seem overly fastidious, but I work at a nuclear weapons plant where
"anal" is never mentioned because it's a given.
J. Scott Mitchell, PE
Fire Protection Engineer |
Projects Engineering
CNS Pantex | 806.477.5883 |
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Duane Johnson
Sent: Monday, January 18, 2016 3:00 PM
To: [email protected]
Subject: RE: Ductile Iron Fittings
The DI standards for pipes and fittings are listed in Chapt 10, Underground
Piping.
Duane Johnson, PE
Design Manager
Strickland Fire Protection
5113 Berwyn Road
College Park, MD 20740
301-474-1136 Office
301-455-0010 Cell
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Monday, January 18, 2016 3:52 PM
To: [email protected]
Subject: RE: Ductile Iron Fittings
B16.4 is for gray iron which I think is the most common form for fire sprinkler
system above ground threaded fittings.
I'm attempting to determine the applicable standard for ductile iron flanged
fittings AND whether or not such fittings are permissible in the above ground
portion of the fire sprinkler system. Specifically in the riser manifold. It
could be a flanged ductile iron tee or flanged ductile iron spool piece, etc.
I heard that they are being used as I described. So, I thought I'd look it up
to see if NFPA 13 allowed it. And, none of the standards listed in the
acceptable materials table address ductile iron.
I'm comfortable with pointing to 1.7 as a "back up" justification. But, any
more help would be appreciated.
J. Scott Mitchell, PE
Fire Protection Engineer |
Projects Engineering
CNS Pantex | 806.477.5883 |
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Matthew J Willis
Sent: Monday, January 18, 2016 2:29 PM
To: [email protected]
Subject: RE: Ductile Iron Fittings
Scott,
Isn't 36.10M for Welded and Seamless pipe?
B16.4 is for fittings.
R/
Matt
Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
*NEW ADDRESS*
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Monday, January 18, 2016 7:27 AM
To: [email protected]
Subject: RE: Ductile Iron Fittings
Thanks for all the responses.
The reason is because NFPA 13 does not include ductile iron (ASME B36.10M) in
the acceptable materials table. My opinion is that it is functionally more than
adequate.
Would this be covered by section 1.7 (2016) for alternate arrangements?
J. Scott Mitchell, PE
Fire Protection Engineer |
Projects Engineering
CNS Pantex | 806.477.5883 |
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org