One jurisdiction around here, requires DI on anything before the backflow.
Basically running the underground inside the building up to the backflow.
NFPA 24, uses the AWWA approvals.

David Autry

Meininger Fire Protection
2521 West L Street, Suite 5
Lincoln, NE 68522
402.466.2616
402.466.2617 fax
[email protected]

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Mike
Hairfield
Sent: Monday, January 18, 2016 2:55 PM
To: [email protected]
Subject: RE: Ductile Iron Fittings

How about AWWA?
Mike

> From: [email protected]
> To: [email protected]
> Subject: RE: Ductile Iron Fittings
> Date: Mon, 18 Jan 2016 20:52:14 +0000
>
> B16.4 is for gray iron which I think is the most common form for fire
sprinkler system above ground threaded fittings.
>
> I'm attempting to determine the applicable standard for ductile iron
flanged fittings AND whether or not such fittings are permissible in the
above ground portion of the fire sprinkler system.  Specifically in the
riser manifold. It could be a flanged ductile iron tee or flanged ductile
iron spool piece, etc.
>
> I heard that they are being used as I described.  So, I thought I'd look
it up to see if NFPA 13 allowed it.  And, none of the standards listed in
the acceptable materials table address ductile iron.
>
> I'm comfortable with pointing to 1.7 as a "back up" justification.  But,
any more help would be appreciated.
>
>     J. Scott Mitchell, PE
>        Fire Protection Engineer |
>        Projects Engineering
>        CNS Pantex | 806.477.5883 |
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> Matthew J Willis
> Sent: Monday, January 18, 2016 2:29 PM
> To: [email protected]
> Subject: RE: Ductile Iron Fittings
>
> Scott,
>
> Isn't 36.10M for Welded and Seamless pipe?
> B16.4  is for fittings.
>
> R/
> Matt
>
> Matthew J. Willis
> Project Manager
> Rapid Fire Protection Inc.
> *NEW ADDRESS*
> 1530 Samco Road
> Rapid City, SD 57702
> Office-605.348.2342
> Direct Line-605.593.5063
> Cell-605.391.2733
> Fax:-605.348.0108
>
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Monday, January 18, 2016 7:27 AM
> To: [email protected]
> Subject: RE: Ductile Iron Fittings
>
> Thanks for all the responses.
>
> The reason is because NFPA 13 does not include ductile iron (ASME
B36.10M) in the acceptable materials table. My opinion is that it is
functionally more than adequate.
>
> Would this be covered by section 1.7 (2016) for alternate arrangements?
>
>     J. Scott Mitchell, PE
>        Fire Protection Engineer |
>        Projects Engineering
>        CNS Pantex | 806.477.5883 |
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
                                        
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to