You protect laundry and trash chutes.There's always a way to do it.

Bob Mahoney402 510 4880

-------- Original message --------
From: Matthew J Willis <[email protected]> 
Date: 03/04/2016  11:45 AM  (GMT-06:00) 
To: [email protected] 
Subject: RE: Shooting Range 

What exactly seems "not right"?

The velocity or projectiles have nothing to do with it. Piping will not even 
hold up.

I feel your case hinges on required or not. FM is calling for it so..

R/

Matt

Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
*NEW ADDRESS*
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jay Stough
Sent: Friday, March 4, 2016 10:43 AM
To: Sprinkler Forum <[email protected]>
Subject: Shooting Range

I am looking for guidance on designing sprinklers in a shooting range.
Something about little glass bulbs or solder links in an area that has high 
velocity projectiles, seems not right.  Everything in each alley (including the 
separation walls) are non-combustible.  The only thing combustible at the end 
of the range is shredded rubber used to absorb the impact after the target.  
The rubber is treated with flame retardant and replaced every three months.  
Each alley has a series of baffles below the roof that are at a 45 degree angle 
for sound.  The designer of the facility has done many of these without 
sprinklers in this area of the building.  He has even shot tracers to see how 
the flame retardant hold up and the flame goes out is less than 20 seconds.  A 
fire marshal is saying to sprinkler everything.
  If you have any insight, I am listening closely.

*Jay Stough*
NICET IV LAYOUT
NICET III ITM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to