I can't see any real justification for smoke detection in the shooting lane 
areas, period.  I see it as a total waste of money. Those areas are constantly 
filled with smoke of varying degrees.  Setting a "normal" threshold would be a 
tremendously wild guess.  

The only even remotely logical areas to use SD if it was tied to a PA type 
sprinkler system would be at the trap end if there were combustibles there and 
at the staging end where you have trash cans but even there the chance of 
anything happening that could initiate a fire is so remote.   Of the places I 
seen, only the sales areas have sprinklers that I can recall, don't remember 
seeing anything in the actual shooting lane part of the facilities.

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Charles Thurston [mailto:[email protected]] 
Sent: Monday, March 07, 2016 11:19 AM
To: Prahl, Craig/SPB <[email protected]>; 
[email protected]
Subject: Re: Shooting Range

Hello Craig,

IF there is a ceiling with space above. This actually this would be a good 
application for Aspirating Smoke Detection. All you would have on the ceiling 
is a small round circle.

Monday, March 7, 2016, 8:26:55 AM, you wrote:

> I had one where the saw tooth roof system was used, it was actually 
> baffles for sound but sprinklers and lines were run behind them.

> The other option which may or may not work is to invoke the Sprinkler 
> Exemption section out of the IBC.  As much as we like to see buildings 
> fully protected, there are cases where is impractical or at times 
> creates a much greater hazard than a fire would.  (yes I've had a 
> project where a fire in the building caused less monetary damage than 
> sprinkler discharge on the process equipment)

> So If you apply Exemptions (2) and (4) out of IBC 903.3.1.1.1 (using 
> the 2012 edition here)

> IBC 2012 903.3.1.1.1 Exempt locations. Automatic sprinklers shall not 
> be required in the following rooms or areas where such rooms or areas 
> are protected with an approved automatic fire detection system in 
> accordance with Section 907.2 that will respond to visible or 
> invisible particles of combustion. Sprinklers shall not be omitted 
> from any room merely because it is damp, of fire-resistance-rated 
> construction or contains electrical equipment.

> 2. Any room or space where sprinklers are considered undesirable 
> because of the nature of the contents, when approved by the fire code 
> official.

> 4. Rooms or areas that are of noncombustible construction with wholly 
> noncombustible contents.

> Now of course there is a trade out of smoke detection for sprinklers 
> which in a gun range isn't going to work either.  There is no real 
> justification for sprinklers in the range areas, maybe at the trap end 
> and maybe at the staging end but down the lanes, there is none.

> But if the AHJ insists on sprinklers then the owner or GC needs to 
> provide some means of protecting the piping and the sprinklers 
> otherwise SIPA or DIPA with dry pilot heads not smoke detection for 
> the trigger is probably going to be the only viable choice.

> Craig L. Prahl
> Fire Protection Group Lead/SME
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]



> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of Michael 
> Hill
> Sent: Friday, March 04, 2016 12:56 PM
> To: [email protected]
> Subject: RE: Shooting Range

> I have put sprinklers in several shooting ranges (Government made me do it).
> They were all double interlock preaction systems with piping run
> above the steel roof/ceiling of the range. They all used concealed type 
> sprinklers.
> One of the ranges utilized a saw tooth ceiling/roof to protect the heads.
> Two of the systems have been hit and put into trouble (including
> the saw tooth one - hit by a ricochet). Luckily no water has been
> released. I know one system that has been hit several times and the
> building has turned the system off.

> Mike Hill

> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]]
> On Behalf Of Jay Stough
> Sent: Friday, March 04, 2016 12:43 PM
> To: Sprinkler Forum <[email protected]>
> Subject: Shooting Range

> I am looking for guidance on designing sprinklers in a shooting range.
> Something about little glass bulbs or solder links in an area that
> has high velocity projectiles, seems not right.  Everything in each
> alley (including the separation walls) are non-combustible.  The
> only thing combustible at the end of the range is shredded rubber
> used to absorb the impact after the target.  The rubber is treated
> with flame retardant and replaced every three months.  Each alley
> has a series of baffles below the roof that are at a 45 degree angle
> for sound.  The designer of the facility has done many of these
> without sprinklers in this area of the building.  He has even shot
> tracers to see how the flame retardant hold up and the flame goes out is less 
> than
> 20 seconds.  A fire marshal is saying to sprinkler everything.
>   If you have any insight, I am listening closely.

> *Jay Stough*
> NICET IV LAYOUT
> NICET III ITM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-- 
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to