I had one where the saw tooth roof system was used, it was actually baffles for 
sound but sprinklers and lines were run behind them.

The other option which may or may not work is to invoke the Sprinkler Exemption 
section out of the IBC.  As much as we like to see buildings fully protected, 
there are cases where is impractical or at times creates a much greater hazard 
than a fire would.  (yes I've had a project where a fire in the building caused 
less monetary damage than sprinkler discharge on the process equipment)

So If you apply Exemptions (2) and (4) out of IBC 903.3.1.1.1 (using the 2012 
edition here) 

IBC 2012 903.3.1.1.1 Exempt locations. Automatic sprinklers shall not be 
required in the following rooms or areas where such rooms or areas are 
protected with an approved automatic fire detection system in accordance with 
Section 907.2 that will respond to visible or invisible particles of 
combustion. Sprinklers shall not be omitted from any room merely because it is 
damp, of fire-resistance-rated construction or contains electrical equipment.

2. Any room or space where sprinklers are considered undesirable because of the 
nature of the contents, when approved by the fire code official.

4. Rooms or areas that are of noncombustible construction with wholly 
noncombustible contents.

Now of course there is a trade out of smoke detection for sprinklers which in a 
gun range isn't going to work either.  There is no real justification for 
sprinklers in the range areas, maybe at the trap end and maybe at the staging 
end but down the lanes, there is none.  

But if the AHJ insists on sprinklers then the owner or GC needs to provide some 
means of protecting the piping and the sprinklers otherwise SIPA or DIPA with 
dry pilot heads not smoke detection for the trigger is probably going to be the 
only viable choice.  

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Michael Hill
Sent: Friday, March 04, 2016 12:56 PM
To: [email protected]
Subject: RE: Shooting Range

I have put sprinklers in several shooting ranges (Government made me do it).
They were all double interlock preaction systems with piping run above the 
steel roof/ceiling of the range. They all used concealed type sprinklers.
One of the ranges utilized a saw tooth ceiling/roof to protect the heads.
Two of the systems have been hit and put into trouble (including the saw tooth 
one - hit by a ricochet). Luckily no water has been released. I know one system 
that has been hit several times and the building has turned the system off.

Mike Hill

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jay Stough
Sent: Friday, March 04, 2016 12:43 PM
To: Sprinkler Forum <[email protected]>
Subject: Shooting Range

I am looking for guidance on designing sprinklers in a shooting range.
Something about little glass bulbs or solder links in an area that has high 
velocity projectiles, seems not right.  Everything in each alley (including the 
separation walls) are non-combustible.  The only thing combustible at the end 
of the range is shredded rubber used to absorb the impact after the target.  
The rubber is treated with flame retardant and replaced every three months.  
Each alley has a series of baffles below the roof that are at a 45 degree angle 
for sound.  The designer of the facility has done many of these without 
sprinklers in this area of the building.  He has even shot tracers to see how 
the flame retardant hold up and the flame goes out is less than
20 seconds.  A fire marshal is saying to sprinkler everything.
  If you have any insight, I am listening closely.

*Jay Stough*
NICET IV LAYOUT
NICET III ITM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to