I would say it depends on how many tiles are missing.  Keep in mind that a new 
installation can have 2x4 openings (aka air return grills).  Although 13 allows 
20% of the overall plane to be open, they can’t be all in one portion of the 
ceiling.  Fall back on the if the opening length is >4 ft the width can not 
exceed 8 inches.

Hopefully this ultra conservative requirement will change next cycle since it 
pretty much kills the allowance regarding floating clouds (and such a 
conservative position is not supported by the Research Foundation’s report).

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On Mar 31, 2016, at 5:32 AM, Jay Stough <[email protected]> wrote:
> 
> We are having a discussion as to whether missing ceiling tiles are a
> deficiency in NFPA 25.  It does not specifically mention it, but it is a
> non-critical deficiency if it is missing escutcheons and cover plates on
> semi-recessed, recessed and concealed sprinklers.  Wouldn't missing ceiling
> tiles create the same problem in a room with a drop ceiling?  I would think
> it would really screw up the air flow of heat to the sprinklers if there
> are 2' X 2' or 2' X 4' holes in the ceilings.
> 
> *Jay Stough*
> NICET IV LAYOUT
> NICET III ITM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to