Agree about discovering, but as I said a few days ago something like~ fire
size determines tenability conditions,  and fire size is based on sprk
height, spacing, temp rating, and RTI

Have I completely lost my mind?
On Apr 18, 2016 3:15 PM, "Duane Johnson" <[email protected]>
wrote:

> Dear Brad,
>
> If smoke detectors cannot catch (meaning to discover) a fire, why do we
> use them to initiate elevator recall before using heat detectors to shunt
> the power? Smoke detectors are very effective in discovering products of
> combustion.
>
> ***Please note our new address***
>
> Duane Johnson, PE
> Design Manager
> Strickland Fire Protection
> 4011 Penn Belt Place
> Forestville, MD 20747
> 301-474-1136 Office
> 301-455-0010 Cell
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brad
> Casterline
> Sent: Monday, April 18, 2016 3:54 PM
> To: [email protected]
> Subject: RE: [EXTERNAL] Re: Fire Sprinkler Plan to Match Evacuation Plan??
>
> Dear Duane,
>
> Smoke detectors are powerless to 'catch a fire', early or late, in terms
> of its size and production of immobilizing products of combustion. What
> they do is start smoke exhaust MUCH earlier than sprinkler flow switches,
> and as it is smoke that kills more people than heat, I say more power to
> them, if there are exhaust fans.
>
> Brad
> On Apr 18, 2016 2:11 PM, "Duane Johnson" <[email protected]>
> wrote:
>
> > Smoke exhaust will use smoke as the fire signature (not heat) as the
> > means to start the fans. The intent is to catch the fire early and
> > prevent untenable situations. The quickest detectable fire signature
> > for this scenario will be smoke, not heat (although there is more to
> > the story, but just keeping it simple for this discussion). Typically
> > there are duct detectors to detect the smoke. There are also local
> > application smoke detectors near openings in the smoke barriers that
> > will automatically close the doors to prevent smoke migration from one
> compartment to the other.
> > There may also be smoke detection throughout the smoke compartment.
> > The whole purpose is to keep adjacent areas tenable to allow zoned
> evacuation.
> > If the adjacent areas becomes untenable, then an evacuation message
> > will annunciate in that zone as well. Not to mention if it becomes
> > untenable the entire fire safety plan has failed.
> >
> > ***Please note our new address***
> >
> > Duane Johnson, PE
> > Design Manager
> > Strickland Fire Protection
> > 4011 Penn Belt Place
> > Forestville, MD 20747
> > 301-474-1136 Office
> > 301-455-0010 Cell
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]] On Behalf Of Brad
> > Casterline
> > Sent: Monday, April 18, 2016 2:58 PM
> > To: [email protected]
> > Subject: RE: [EXTERNAL] Re: Fire Sprinkler Plan to Match Evacuation
> Plan??
> >
> > Peter,
> >
> > Is it true that the 'smoke protected' systems you refer to require
> > smoke detectors? If you are waiting 2 or 3 minutes for a sprinkler to
> > operate, and add a 60 second flow switch retard feature, plus if there
> > are exhast fans a 10 second ramp-up to full strength, these defend in
> > place safe areas adjacent to the origin are already likely untenable.
> > And you mentioned non-sprinklered facilities, so wouldn't the same
> > Smoke, Evac, and FA matching footprint rules apply whether there were
> > flow switches or not?
> > Just curious, Brad
> > On Apr 18, 2016 1:35 PM, "Larrimer, Peter A" <[email protected]>
> > wrote:
> >
> > > There must be one water flow alarm switch per smoke zone.  When we
> > > "defend in place" or defend in a safe place, that safe place is
> > > usually a smoke zone that is separate from the zone of fire origin.
> > > If there is only one sprinkler switch on a floor and there happens
> > > to be three smoke zones, the one sprinkler switch cannot be
> > > programmed to identify anything other than the floor.  In that
> > > scenario, an alarm would not be able to be programmed to tell staff
> > > where the fire is located.  Staff would only be able to be directed
> > > to the floor and not the smoke zone of fire origin.  Ideally, the
> > > sprinklers would be fed from three risers through three separate
> > > flow switches so that the signal sent over the fire alarm system
> > > would identify the zone of fire origin to the staff.  Each sprinkler
> > > tends to serves as an initiating device to the fire alarm system
> through its respective flow switch.
> > >
> > > The VA intends to provide one sprinkler zone per each smoke zone for
> > > the reasons stated above.  The codes are not specific on the details.
> > > Some could argue that multiple smoke zones within a single sprinkler
> > > zone could be provided and it would be compliant with the codes that
> > > I have referenced.  I don't disagree.  However, how does the
> > > facility try to write a fire plan and explain to staff that the fire
> > > alarm system will tell you where to go when there is an alarm unless
> > > the alarm is activated by the sprinkler system alarm in which case
> > > the system can only tell you the floor where the fire is and not the
> zone.
> > > It just makes it difficult for our personnel to respond quickly to a
> > fire.
> > >
> > > Note:  A sprinkler system could be installed in a two story
> > > healthcare building (defend in place) that has 3 or more smoke zones
> > > per floor and have only one water flow switch for the whole building
> > > and the installation would be in compliance with NFPA 13.
> > > Unfortunately, if the fire alarm system was initiated by the
> > > sprinkler system water flow switch, the fire alarm system would not
> > > be able to identify the fire origin since the one and only switch
> > > would be activated for any
> > sprinkler in the building.
> > >  Where would the staff go to help assist with patient relocation?
> > >
> > > Hope this helps.
> > >
> > > Peter Larrimer
> > > VA
> > >
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum [mailto:
> > > [email protected]] On Behalf Of
> > > [email protected]
> > > Sent: Monday, April 18, 2016 12:05 PM
> > > To: [email protected]
> > > Subject: RE: [EXTERNAL] Re: Fire Sprinkler Plan to Match Evacuation
> > Plan??
> > >
> > > Hi Peter,
> > >
> > > I have two related questions on your response, for clarification.
> > >
> > > First question: When you say "However, the fire alarm system can
> > > only send the proper alarm signal from a sprinkler system if the
> > > sprinkler system has a water flow switch per zone."  Do you intend
> > > that to mean, "if the sprinkler system has a water flow switch per
> > > "smoke zone", or per "sprinkler zone"?
> > >
> > > Second question: When you say "Therefore, VA requires the sprinkler
> > > zones to be coincidental with the smoke zones...". Do you intend
> > > that to mean "one sprinkler zone=one smoke zone" or "one sprinkler
> > > zone= one or more smoke zones", and that the boundary of the
> > > sprinkler zone coincides with the boundary of all encompassed smoke
> zones.
> > >
> > > Based upon your reference to NFPA 99,  "15.7.4.3.1* Where buildings
> > > are required to be subdivided into smoke compartments, fire alarm
> > > notification zones shall coincide with one or more smoke compartment
> > > boundaries or shall be in accordance with the facility fire plan.",
> > > it appears to me that the correct answer to the first question is
> > > "sprinkler zone", and the second question is  "one sprinkler zone=
> > > one
> > or more smoke zones".
> > >
> > > Mark at Aero
> > > 602 820-7894
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl er.org _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> > > er.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to