I have two related questions on your response, for clarification.

First question: When you say "However, the fire alarm system can only send the 
proper alarm signal from a sprinkler system if the sprinkler system has a water 
flow switch per zone."  Do you intend that to mean, "if the sprinkler system 
has a water flow switch per "smoke zone", or per "sprinkler zone"?

Second question: When you say "Therefore, VA requires the sprinkler zones to be 
coincidental with the smoke zones...". Do you intend that to mean "one 
sprinkler zone=one smoke zone" or "one sprinkler zone= one or more smoke 
zones", and that the boundary of the sprinkler zone coincides with the boundary 
of all encompassed smoke zones.

Based upon your reference to NFPA 99,  "15.7.4.3.1* Where buildings are 
required to be subdivided into smoke compartments, fire alarm notification 
zones shall coincide with one or more smoke compartment boundaries or shall be 
in accordance with the facility fire plan.", it appears to me that the correct 
answer to the first question is "sprinkler zone", and the second question is  
"one sprinkler zone= one or more smoke zones".

Mark at Aero
602 820-7894