The original building was built in 1884 and the sprinkler system installed at that time. Since the standardized pipe schedule did not come into being until 1896, my assumption is that the sizing was at the installers discretion. The branch pipe sizing is less that what was called for in 1896 edition of the sprinkler standard (3/4-1-1-1.1/4-1.1/4, etc). I seriously doubt that this would meet a hydraulic calculation. However, this system has been great-great-grandfathered in so far.
My plan is to write a letter to the owner's agent.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Wed, Apr 27, 2016 at 9:01 AM, Scott Futrell <[email protected]> wrote:
Good morning Todd.



It is my opinion that you need to notify someone that an evaluation in accordance with NFPA 25 (2014 edition) 4.1.6 and 4.1.7 needs to be undertaken. Code of Ethics. If you've seen it, as a FPE, you are obligated to question it if it doesn't appear to be correct.



It would take some research to determine what edition of NFPA 13 was applicable at the time of the original construction and if there was a change in occupancy for the 12 ft. storage. But, protecting 12 ft. of class IV without a calculation to verify the water supply versus the pipe schedule pipe sizing could be problematic.



As far as the fire department approving it goes, from the 2012 IFC, 105.3.6 Compliance with Code. The issuance or granting of a permit shall not be construed to be a permit for, or an approval of, any violation of any of the provisions of this code or of any other ordinance of the jurisdiction. Permits presuming to give authority to violate or cancel the provisions of this code or other ordinances of the jurisdiction shall not be valid...Any addition to or alteration of approved construction documents shall be approved in advance by the fire code official, as evidenced by the issuance of a new or amended permit. 105.4.4 Approved documents. Construction documents approved by the fire code official are approved with the intent that such construction documents comply in all respects with the code. Review and approval by the fire code officials shall not relieve the applicant of the responsibility of compliance with this code. [emphasis added]



If it is designed, installed, tested, inspected, and maintained incorrectly it is still wrong.



Good luck.



Scott



Office: (763) 425-1001 x 2

Cell: (612) 759-5556



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, April 27, 2016 5:28 AM
To: [email protected]
Subject: Existing pipe schedule and storage



I am working at a facility where there is an existing OH pipe schedule system over 12ft palletized Class IV storage. The fire department has approved it, but I question whether it will provide adequate protection. I did not see anything in NFPA 13 that requires storage occupancies to be hydraulically calculated. Am I missing something?

This is outside of the project I am working on, but as an FPE, I feel obligated to notify someone if I see a potential hazard such as this.



Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT

860-535-2080 (ofc) 860-608-4559 (cell)

Sent using CloudMagic

[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]

_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to