I understand the concerns, but first of all, I am going to the owner's rep, not 
the AHJ. They may have an analysis, but I have my doubts (I would have most 
likely been asked to do it). The letter can die with the rep, but at least I 
would have done my part.
This is not an OH Pipe Schedule system as we know it. The system was installed 
8 years before the first edition of the Rules and Regulations for Sprinkler 
Equipments (now NFPA 13) came out. It is an early version of some kind of pipe 
schedule (ex: up to 10 sprinklers fed from 1-1/2") possibly created by the 
installing contractor. I am pretty confident that the occupancy has changed for 
two reasons: First, there was probably not a lot of demand for free-flowing 
plastic pellets in a textile mill in 1884, when the building was constructed. 
Secondly, I was in this building 8 to 10 years ago and I remember the basement 
as being vacant. Roland is right that this is not going to calc out and any 
attempt to do so is just going to create a fecal storm.
My beef here is that the existing sprinkler system is probably not going to do 
too much to control a fire with this occupancy. It might send an alarm. This 
could end up in another classic mill fire as there are 3 stories above it. I 
really don't want to see that.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic 
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Wed, Apr 27, 2016 at 1:54 PM, Roland Huggins <[email protected]> 
wrote:
This poses an interesting dilemma. You feel it is a problem but can’t 
articulate a definitive statement so do you or don’t you write a letter. I 
certainly understand the need for a CYA philosophy (as moronic and insane as 
our legal system has become - notice I didn’t say anything about justice since 
that is not what the courts provide). But I’m off path.

The interesting dilemma is that you have a pipe schedule system acceptable for 
protecting an Ordinary Hazard classification. You have a storage facility that 
can be protected as an OHG2 (aka not treated as storage but as a chap 11 risk). 
Any discussion on it not calculating out is a nonstarter since pipe schedule 
systems never calc-out (after all a calculated system was based on supplying a 
remote area in a pipe schedule layout about 2/3 the distance out from the 
riser).

So the big question is where’s the beef?


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On Apr 27, 2016, at 3:27 AM, Todd Williams <[email protected]> wrote:
>
> I am working at a facility where there is an existing OH pipe schedule system 
> over 12ft palletized Class IV storage. The fire department has approved it, 
> but I question whether it will provide adequate protection. I did not see 
> anything in NFPA 13 that requires storage occupancies to be hydraulically 
> calculated. Am I missing something?
> This is outside of the project I am working on, but as an FPE, I feel 
> obligated to notify someone if I see a potential hazard such as this.
>
> Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 
> 860-535-2080 (ofc) 860-608-4559 (cell)
> Sent using CloudMagic 
> [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to