NFPA 22 is not referenced in NFPA 13D so it doesn't apply just as NFPA 24
isn't referenced and so doesn't apply to underground lead-ins in SFDs.
These guys get a little crazy sometimes. There is a jurisdiction here that
wants sprinklers in garages that uses the IBC-S2/NFPA-OH1 path for
guidance. That leaves us with a density and duration on an SFD garage that
meets the criteria fro a commercial parking structure.

On Fri, May 13, 2016 at 7:00 AM, Tim Stone <[email protected]> wrote:

> Are there any requirements in NFPA 22 not allowing the use of Polyethylene
> water storage tanks for residential or commercial sprinkler systems? These
> tanks are installed above ground usually in Basements.
>
> The local State agency is getting ready to adopt the 2013 edition of NFPA
> 22 and I am being told NFPA 22 only permits Fiberglass. I don’t see where
> Polyethylene is excluded.
>
>
>
> Thoughts please.
>
>
>
> Regards,
>
> *G. Tim Stone*
>
>
>
> *G. Tim Stone Consulting, LLC*
>
> *NICET Level III Engineering Technician*
>
> *Fire Protection Sprinkler Design*
>
> *and Consulting Services*
>
>
>
> *                117 Old Stage Rd. - Essex Jct., VT. 05452*
>
> *CELL: (802) 373-0638 <%28802%29%20373-0638>   TEL: (802) 434-2968
> <%28802%29%20434-2968>   Fax: (802) 434-4343 <%28802%29%20434-4343>*
>
>                            [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to