NFPA 22 is not referenced in NFPA 13D so it doesn't apply just as NFPA 24 isn't referenced and so doesn't apply to underground lead-ins in SFDs. These guys get a little crazy sometimes. There is a jurisdiction here that wants sprinklers in garages that uses the IBC-S2/NFPA-OH1 path for guidance. That leaves us with a density and duration on an SFD garage that meets the criteria fro a commercial parking structure.
On Fri, May 13, 2016 at 7:00 AM, Tim Stone <[email protected]> wrote: > Are there any requirements in NFPA 22 not allowing the use of Polyethylene > water storage tanks for residential or commercial sprinkler systems? These > tanks are installed above ground usually in Basements. > > The local State agency is getting ready to adopt the 2013 edition of NFPA > 22 and I am being told NFPA 22 only permits Fiberglass. I don’t see where > Polyethylene is excluded. > > > > Thoughts please. > > > > Regards, > > *G. Tim Stone* > > > > *G. Tim Stone Consulting, LLC* > > *NICET Level III Engineering Technician* > > *Fire Protection Sprinkler Design* > > *and Consulting Services* > > > > * 117 Old Stage Rd. - Essex Jct., VT. 05452* > > *CELL: (802) 373-0638 <%28802%29%20373-0638> TEL: (802) 434-2968 > <%28802%29%20434-2968> Fax: (802) 434-4343 <%28802%29%20434-4343>* > > [email protected] > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > -- Ron Greenman 4110 Olson Dr., NW Gig Harbor, WA 98335 [email protected] 253.576.9700 A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958)
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org