Tim,

Ron is correct about the residential tank - NFPA-22 does not apply to 13-D 
systems.

As for the limits on tank materials, it is true that sec. 4.4 limits materials 
to steel, wood, concrete, coated fabrics, and fiberglass-reinforced plastic.

However, there is always the equivalency clause in 1.4.  The AHJ can approve a 
tank that can be shown to have equivalency in quality strength, fire 
resistance, effectiveness, durability and safety. Someone just has to provide 
the documentation to the AHJ for their approval.

My opinion only and not an official position of the NFPA-22 Technical Committee.


Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tim Stone
Sent: Friday, May 13, 2016 9:00 AM
To: [email protected]
Subject: Polyethylene Tanks

Are there any requirements in NFPA 22 not allowing the use of Polyethylene 
water storage tanks for residential or commercial sprinkler systems? These 
tanks are installed above ground usually in Basements.
The local State agency is getting ready to adopt the 2013 edition of NFPA 22 
and I am being told NFPA 22 only permits Fiberglass. I don't see where 
Polyethylene is excluded.

Thoughts please.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]<mailto:[email protected]>


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to