Ron,

 

My original post was including 13R systems not 13Ds. 

After I wrote I went back through NFPA 22 and found section 4.4 “Tank 
Material”. The 2013 edition of NFPA 13R now refers us to NFPA 22 if tanks are 
to be used. 

 

Maybe the State will allow us the equivalency clause in 1.4. 

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                            <mailto:[email protected]> [email protected]

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Friday, May 13, 2016 10:20 AM
To: [email protected]
Subject: Re: Polyethylene Tanks

 

NFPA 22 is not referenced in NFPA 13D so it doesn't apply just as NFPA 24 isn't 
referenced and so doesn't apply to underground lead-ins in SFDs. These guys get 
a little crazy sometimes. There is a jurisdiction here that wants sprinklers in 
garages that uses the IBC-S2/NFPA-OH1 path for guidance. That leaves us with a 
density and duration on an SFD garage that meets the criteria fro a commercial 
parking structure. 

 

On Fri, May 13, 2016 at 7:00 AM, Tim Stone <[email protected] 
<mailto:[email protected]> > wrote:

Are there any requirements in NFPA 22 not allowing the use of Polyethylene 
water storage tanks for residential or commercial sprinkler systems? These 
tanks are installed above ground usually in Basements. 

The local State agency is getting ready to adopt the 2013 edition of NFPA 22 
and I am being told NFPA 22 only permits Fiberglass. I don’t see where 
Polyethylene is excluded.

 

Thoughts please.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL:  <tel:%28802%29%20373-0638> (802) 373-0638   TEL:  
<tel:%28802%29%20434-2968> (802) 434-2968   Fax:  <tel:%28802%29%20434-4343> 
(802) 434-4343

                            <mailto:[email protected]> [email protected]

 


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





 

-- 

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected] <mailto:[email protected]> 

253.576.9700

 

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to