I wouldn't go for 2" X 6"'s with a visqueen liner, but if you want 13-D water 
supply has always been the deal breaker. I guess there are tanks and there are 
tanks, but I'd look favorably on a substantial polyethylene tank.

Bruce Verhei



> On May 13, 2016, at 07:32, Mark A. Sornsin, P.E. <[email protected]> 
> wrote:
> 
> Tim,
>  
> Ron is correct about the residential tank – NFPA-22 does not apply to 13-D 
> systems.
>  
> As for the limits on tank materials, it is true that sec. 4.4 limits 
> materials to steel, wood, concrete, coated fabrics, and fiberglass-reinforced 
> plastic.
>  
> However, there is always the equivalency clause in 1.4.  The AHJ can approve 
> a tank that can be shown to have equivalency in quality strength, fire 
> resistance, effectiveness, durability and safety. Someone just has to provide 
> the documentation to the AHJ for their approval.
>  
> My opinion only and not an official position of the NFPA-22 Technical 
> Committee.
>  
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer 
> | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | KFIengineers.com
> 
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Tim Stone
> Sent: Friday, May 13, 2016 9:00 AM
> To: [email protected]
> Subject: Polyethylene Tanks
>  
> Are there any requirements in NFPA 22 not allowing the use of Polyethylene 
> water storage tanks for residential or commercial sprinkler systems? These 
> tanks are installed above ground usually in Basements.
> The local State agency is getting ready to adopt the 2013 edition of NFPA 22 
> and I am being told NFPA 22 only permits Fiberglass. I don’t see where 
> Polyethylene is excluded.
>  
> Thoughts please.
>  
> Regards,
> G. Tim Stone
>  
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
>  
>                 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                            [email protected]
>  
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to