So not the Tee, Charles?

On Tue, May 17, 2016 at 8:37 PM, Charles Thurston <[email protected]>
wrote:

> Hello rongreenman,
>
> The restriction is in the casting for the body of the valve. I have seen
> it and warned my guys to be very careful cleaning the seats.
>
> Tuesday, May 17, 2016, 9:38:12 PM, you wrote:
>
> > I'm surprised that something this unusual isn't even listed as a special
> part on the cut sheets. They just say ¾" x whatever x whatever. Purpose of
> the restriction?
>
>
> > Talk to Tyco.
>
> > On Tue, May 17, 2016 at 6:35 PM, Scott Futrell <[email protected]> wrote:
>
> >
> >
> >
> > Ron,
> >
> >
> >
> > Nope, it’s designed that way. I’ve asked fitters to look, and I’ve
> looked at new ones off the truck. That’s the way it comes. Data sheet
> doesn’t show it, or say anything  about it.
> >
> >
> >
> > Nope.
> >
> >
> >
> > I’m thinking most don’t realize this, and most don’t realize wiping off
> the seat pushes the gunk into the slot that leads to the two holes.
> >
> >
> >
> > Scott
> >
> >
> >
> > Office: (763) 425-1001 x 202
> >
> > Cell: (612) 759-5556
> >
> >
> >
> > From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of rongreenman .
> >  Sent: Tuesday, May 17, 2016 8:31 PM
> >  To: [email protected]
> >  Subject: Re: Tyco Dry Pipe Valve
> >
> >
> >
> >
> > Maybe just a bad casting. Nothing about that in the cut sheet and that
> would be some neon flashing sign if there was a special tee in the alarm
> line.
> >
> >
> >
> >
> >
> > Have you talked to Tyco?
> >
> >
> >
> >
> >
> > As an example of this Viking has special ball drips that work only on
> designated valve trims. One that will not work with a DPV may be for a
> deluge valve.The info for this is glaring when you actually go looking for
> it. http://www.vikinggroupinc.com/databook/checkvalves/062289.pdf
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> > _______________________________________________
> >  Sprinklerforum mailing list
> >  [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
>
>
>
>
>
> --
> Best regards,
>  Charles                            mailto:[email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to