Curiouser and curiouser. I'm currently doing piece of work in s large food
distribution center. There's a fitter along to play with the toys and all I
do..., well, let's just say not too much.

I mentioned this discussion to him and he nodded with that  " Ifeel you
brother" look and said they're clogged a lot.

On Wednesday, May 18, 2016, Charles Thurston <[email protected]> wrote:

> Hello rongreenman,
>
> Nope it is in the casting for the body.
>
> Wednesday, May 18, 2016, 12:38:06 AM, you wrote:
>
> > So not the Tee, Charles?
>
>
>
> > On Tue, May 17, 2016 at 8:37 PM, Charles Thurston <[email protected]
> <javascript:;>> wrote:
>
> > Hello rongreenman,
> >
> >  The restriction is in the casting for the body of the valve. I have
> seen it and warned my guys to be very careful cleaning the seats.
> >
> >  Tuesday, May 17, 2016, 9:38:12 PM, you wrote:
> >
>  >> I'm surprised that something this unusual isn't even listed as a
> special part on the cut sheets. They just say ¾" x whatever x whatever.
> Purpose of the restriction?
> >
> >
>  >> Talk to Tyco.
> >
>  >> On Tue, May 17, 2016 at 6:35 PM, Scott Futrell <[email protected]
> <javascript:;>> wrote:
> >
>
>
>
>  >> Ron,
>
>
>
>  >> Nope, it’s designed that way. I’ve asked fitters to look, and I’ve
> looked at new ones off the truck. That’s the way it comes. Data sheet
> doesn’t show it, or say anything  about it.
>
>
>
>  >> Nope.
>
>
>
>  >> I’m thinking most don’t realize this, and most don’t realize wiping
> off the seat pushes the gunk into the slot that leads to the two holes.
>
>
>
>  >> Scott
>
>
>
>  >> Office: (763) 425-1001 x 202
>
>  >> Cell: (612) 759-5556
>
>
>
>  >> From: Sprinklerforum [mailto:
> [email protected] <javascript:;>] On Behalf
> Of rongreenman .
>  >>  Sent: Tuesday, May 17, 2016 8:31 PM
>  >>  To: [email protected] <javascript:;>
>  >>  Subject: Re: Tyco Dry Pipe Valve
>
>
>
>
>  >> Maybe just a bad casting. Nothing about that in the cut sheet and that
> would be some neon flashing sign if there was a special tee in the alarm
> line.
>
>
>
>
>
>  >> Have you talked to Tyco?
>
>
>
>
>
>  >> As an example of this Viking has special ball drips that work only on
> designated valve trims. One that will not work with a DPV may be for a
> deluge valve.The info for this is glaring when you actually go looking for
> it. http://www.vikinggroupinc.com/databook/checkvalves/062289.pdf
>
>
>
>
>
>
>
>
>
>
>
>  >> _______________________________________________
>  >>  Sprinklerforum mailing list
>  >>  [email protected] <javascript:;>
>  >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> >
> >
> >
> >
> >
> >
> >
> >
> >  --
> >  Best regards,
> >   Charles                            mailto:[email protected]
> <javascript:;>
> >
> >  _______________________________________________
> >  Sprinklerforum mailing list
> >  [email protected] <javascript:;>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
>
>
>
>
> --
> Best regards,
>  Charles                            mailto:[email protected]
> <javascript:;>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] <javascript:;>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>


-- 
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to