Is the low air switch affected by this design?


> On May 18, 2016, at 13:46, rongreenman . <[email protected]> wrote:
> 
> Curiouser and curiouser. I'm currently doing piece of work in s large food 
> distribution center. There's a fitter along to play with the toys and all I 
> do..., well, let's just say not too much. 
> 
> I mentioned this discussion to him and he nodded with that  " Ifeel you 
> brother" look and said they're clogged a lot. 
> 
>> On Wednesday, May 18, 2016, Charles Thurston <[email protected]> wrote:
>> Hello rongreenman,
>> 
>> Nope it is in the casting for the body.
>> 
>> Wednesday, May 18, 2016, 12:38:06 AM, you wrote:
>> 
>> > So not the Tee, Charles?
>> 
>> 
>> 
>> > On Tue, May 17, 2016 at 8:37 PM, Charles Thurston <[email protected]> 
>> > wrote:
>> 
>> > Hello rongreenman,
>> >
>> >  The restriction is in the casting for the body of the valve. I have seen 
>> > it and warned my guys to be very careful cleaning the seats.
>> >
>> >  Tuesday, May 17, 2016, 9:38:12 PM, you wrote:
>> >
>>  >> I'm surprised that something this unusual isn't even listed as a special 
>> part on the cut sheets. They just say ¾" x whatever x whatever. Purpose of 
>> the restriction?
>> >
>> >
>>  >> Talk to Tyco.
>> >
>>  >> On Tue, May 17, 2016 at 6:35 PM, Scott Futrell <[email protected]> wrote:
>> >
>> 
>> 
>> 
>>  >> Ron,
>> 
>> 
>> 
>>  >> Nope, it’s designed that way. I’ve asked fitters to look, and I’ve 
>> looked at new ones off the truck. That’s the way it comes. Data sheet 
>> doesn’t show it, or say anything  about it.
>> 
>> 
>> 
>>  >> Nope.
>> 
>> 
>> 
>>  >> I’m thinking most don’t realize this, and most don’t realize wiping off 
>> the seat pushes the gunk into the slot that leads to the two holes.
>> 
>> 
>> 
>>  >> Scott
>> 
>> 
>> 
>>  >> Office: (763) 425-1001 x 202
>> 
>>  >> Cell: (612) 759-5556
>> 
>> 
>> 
>>  >> From: Sprinklerforum 
>> [mailto:[email protected]] On Behalf Of 
>> rongreenman .
>>  >>  Sent: Tuesday, May 17, 2016 8:31 PM
>>  >>  To: [email protected]
>>  >>  Subject: Re: Tyco Dry Pipe Valve
>> 
>> 
>> 
>> 
>>  >> Maybe just a bad casting. Nothing about that in the cut sheet and that 
>> would be some neon flashing sign if there was a special tee in the alarm 
>> line.
>> 
>> 
>> 
>> 
>> 
>>  >> Have you talked to Tyco?
>> 
>> 
>> 
>> 
>> 
>>  >> As an example of this Viking has special ball drips that work only on 
>> designated valve trims. One that will not work with a DPV may be for a 
>> deluge valve.The info for this is glaring when you actually go looking for 
>> it. http://www.vikinggroupinc.com/databook/checkvalves/062289.pdf
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>>  >> _______________________________________________
>>  >>  Sprinklerforum mailing list
>>  >>  [email protected]
>>  >>  
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> >
>> >  --
>> >  Best regards,
>> >   Charles                            mailto:[email protected]
>> >
>> >  _______________________________________________
>> >  Sprinklerforum mailing list
>> >  [email protected]
>> >  
>> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> >
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> --
>> Best regards,
>>  Charles                            mailto:[email protected]
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> -- 
> Sent from Gmail Mobile
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to