Yes.  We, as AHJ during system acceptance testing, are finding multiple heads 
with internal glue obstructions.  The heads are (and continue to be on plastic 
jobs) installed prior to the drop being set into place, with glue subsequently 
"dripping" down into the head.

Photo examples if you want them, email me direct.

Sincerely,

Andrew Steele
Fire Marshal,
Dayton Fire Department
300 North Main Street
Dayton, Ohio 45402

(937) 333-4526







From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Wednesday, July 13, 2016 1:10 PM
To: [email protected]
Subject: RE: Visual Inspection of CPVC System

Might even be a tape concern...
R/
Matt

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Wednesday, July 13, 2016 10:59 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Visual Inspection of CPVC System







We recently had a local AHJ require a visual inspection of a CPVC system prior 
to

doing a hydrostatic test.



All places where a sprinkler head was installed they made us remove the heads 
for the inspection.



Has anyone ever had this happen to them or am I missing something here?



Thanks,



Mike