The floor control valves are irrelevant and it can be one system.  One run-in, 
one riser.  30,000 sf per floor.  You're good to go.



Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jeff Bridges
Sent: Thursday, September 01, 2016 2:31 PM
To: [email protected]
Subject: RE: 5 year fire sprinkler Obstruction Assessment - What items in a 
system define it as a separate wet pipe system? [EXTERNAL]

I didn't
I was showing if it all is one system as Ron was eluding to, floor controls not 
considered as separation, the cumulative total of floor space being covered 
under a single riser would be 120K
BUT if floor controls ARE considered as a riser, each RISER is covering 30K.
I never said that 30K is a max per riser but if, under my example, floor 
controls are merely considered making the system easier to drain and not a 
separate system, then it exceeds 52K as allowed.
Right?

Jeff Bridges
JB Fire Protection Inc
(888) 523-4737 Fax (714) 578-0901
Fire Sprinklers Save Lives & Property
www.jbfireprotection.com<http://www.jbfireprotection.com/>

This email transmission (and any of its attachments) is intended only for the 
person or entity to whom it is addressed, and may contain confidential, 
proprietary and/or privileged information. No waiver of any applicable 
privileges or protections is intended hereby. If you are not the person to whom 
this transmission is addressed, you are hereby notified that the disclosure, 
copying, distribution, reliance upon or use of any of the information contained 
in this transmission is strictly prohibited. If you have received this 
transmission in error, delete any copies which may exist on your system and 
notify the sender immediately. This email transmission cannot be guaranteed 
secure or error-free. Any views expressed in this message are those of the 
individual sender, except where the sender specifies them to be the views of 
the company and is authorized to do so.


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Parsley Consulting
Sent: Thursday, September 01, 2016 11:07 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: 5 year fire sprinkler Obstruction Assessment - What items in a 
system define it as a separate wet pipe system?

Jeff,
    I'm kind of curious how you've decided that 30,000 square foot per floor 
exceeds the allowable floor space per riser.  Aren't the values in 8.2.1 
supposed to be applied to any one floor area?
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit our website<http://www.parsleyconsulting.com/>
On 09/01/2016 10:45 AM, Jeff Bridges wrote:
I would respectfully disagree with the below analogy.
Example: (4) Story building consisting of 30K SF per floor
Single lead-in supply- combo standpipe with floor controls.
How can it be considered a single system when it exceeds the allowable floor 
space per riser?
Just sayin'

Jeff Bridges
JBFP Inc




I have to disagree with this analysis that a floor control valve defines a 
system. A floor control valve is not even defined individually in 2013 whereas 
a sprinkler system is (no mention of floor control valves) as are control 
valves. As always, I would consider a system to be what it has always been and 
the addition of the required floor control valve and associated requirements on 
systems in multi-story buildings just nationally codifies a common practice 
hereabouts of building a system that has isolatable floors. This way an entire 
large building does not need to be drained to make a repair or for a T.I., 
leaves fore protection in service on floors not effected and also conserves 
water.  I'm open to an argument that changes my mind but this one doesn't.




_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to